How we can use analog input 2 wire but the transmitter is 2 wire...?
Hence, the analog 2 wire of Siemens Step7 (All analog input module) is 4-20 mA, without changing the transmiter, because the transmitter is 0-20mA.
Are You sure that transmitter is 2 wire because transmitter power supply is provide over this 2 wires. That's why 2 wire transmitters have no possibilities to choose 0..20mA range.
Yes, i am sure about this input analog. The input that i obtain is from a feedback control valve 0..100% = 0..20 mA. It's quite strange, but it's true.
2 Wires transmitter, 1 wire for 24VDC whereby another 1 is for Signal (I+).
If your feedback control valve 0..100% = 0..20 mA.
Then in Simatic Manager Hardware Configuration, you might set the Alalog Input from 4-20mA to 0-20mA. Remembered the Jumper Setting at that Analog Input Module Cards it self must set correctly.