communication s7 400 with premium plc on the profibus
другие контроллеры
ELYAS_GH
Post by ELYAS_GH »
Dear All, Here i have used siemens s7-400 PlC system. I want to communicate the schneider premium plc(TSX57203 processor) on profibus network.
siemens plc is master and premium plc is slave.
Can i know it is possible to communiicate the same on profibus network?
tanks
ALEXZ
Re: communication s7 400 with premium plc on the profibus
Post by ALEXZ »
I think you need Tsx PBY100 module
ELYAS_GH
Post by ELYAS_GH »
Thanks for your cooperation
Are right.
Should I use this module.
It is possible that ،Premium PLC can be defined as Slave?
ALEXZ
Post by ALEXZ »
I have some experiens to use Quantum as master and s7-300 as slave via profibus. I used gateway modbus tcp/profibus dp TCSEGPA23F14F
For Premium I think it's compatible. Maybe you need add ETY ethernet module which will do IO-scanning with that gateway.
zafarictrl
Post by zafarictrl »
hi
you need install GSD file in hardware configuration for s7-400 know your slave.
SE_support
Post by SE_support »
ELYAS_GH wrote:Dear All, Here i have used siemens s7-400 PlC system. I want to communicate the schneider premium plc(TSX57203 processor) on profibus network.
tanks
Hello, you can use TCSEGPA23F14F Profibus Master Module on Premium side. The TCSEGPA23F14F is master and can't be configured as slave, so the SIEMENS PLC should be slave or you must use DP/DP-coupler (pretty slow). The PREMIUM communicates with TCSEGPA23F14F via i/o-scanner, which setting will be automatically set by DTM for TCSEGPA23F14F.
Or you can use modbus/TCP.....