Hello,
I have a:
bar code reader SICK CLV series with a ethernet communication;
PLC CompactLogix 1769-L35E (ethernet communication);
HMI Painel View 1000 Plus (ethernet communication);
Switch hirschmann IP69
All components are linked by switch hirschmann but i can not configure the PLC to read de data of barcode. All other components are Ok and ON
Hi,
Before, you try to send or read data, you have to know if your barecode reader support Ethernet Industrial protocol.(Ethernet/IP)
For example on Ethernet, Siemens and Rockwell cannot communicate :
Siemens use Industrial Ethernet protocol (IE protocol)
Rockwell use Ethernet Industrial protocol.(Ethernet/IP)
In that case you have to use a gateway...
So for you application, you have to verify, which protocol your barecode reader support...
Best regards
Please type the exact barcode reader type. There is a range of CLV62x products with different communication options.
For example: CLV620-0120 supports CAN, Ethernet TCP/IP, and EtherNet/IP available on board, no additional
gateway needed (depending on variant)...
bilbo_321 wrote:Please type the exact barcode reader type. There is a range of CLV62x products with different communication options.
For example: CLV620-0120 supports CAN, Ethernet TCP/IP, and EtherNet/IP available on board, no additional
gateway needed (depending on variant)...
did you found the sample code from SICK web site?
I could upload it to Rapidshare if you have any troubles?
Hello Bilbo
Do you know how to send a string from the Barcode Reader to the PLC
I need to know everything that is related to the comunication of the Barcode Reader and the PLC
And you can upload it to Rapidshare, i have no troubles
Thanks
Hi
I´m Back muahaha
Sorry for the time without answering
Just for close this topic
The technical support the SICK spent a wrong program. With the correct program the communication is established and all components work correctly.