Hi all,
I used to use the SFC101 as a machine hourscounter, but I have seen that everytime the counter is restarted, the minutes go to zero, so it is totally useless, as it only counts entire hours.
I liked that because it is stored in eeprom.
Is there any other system block a little more serious to count the production time including minutes?
[?]: Hourscounter in S7-300
Re: [?]: Hourscounter in S7-300
Hi Scarch!
Look at Siemens entry ID: http://support.automation.siemens.com/W ... en/5504548
sventek
GreetingsHow do you count the runtime elapsed for more than 8 resources?
sventek
Thanks !!
Hi Scarch!
I have used this function:
I hope have been useful
best regards
Arimateia - Brazil
A(
A M 352.2 //auxiliary command enabled
A M 8.0 //machine running
JCN C002
AN M 6.5 //1 second tick positice edge
JC C002
L DB26.DBD 74 //running time since
L 1
+D
T DB26.DBD 74
L 3600
/D
T DB26.DBW 82 //running time since - hours
L DB26.DBD 74
L 3600
MOD
L L#60
/D
T DB26.DBW 84 //running time since - minute
L DB26.DBD 74
L 60
MOD
T DB26.DBW 86 //running time since - second
best regards
Arimateia - Brazil
If you use clock memory, bit 5, it has a period of 1 second. When you detect a rising (or falling) edge in that particular bit, you can increment a counter (dword maybe) by one. So, this counter is counting seconds, up to a maximum of
4294967295 seconds = 136.102208 years. (Even if you don't want to use in hex, even in signed double integer you get half of it: 68 years)
Looks enough to me.
Variations include using interrupts to do the same thing, by a second, minute, anything you like...
Hope this helps
Looks enough to me.
SET
A M 255.5 // clock memory byte M255
FP M 120.0 // auxiliary bit for rising edge
JNB _002
L L#1
L MD 122 // this is your counter
+D
T MD 122 // your counter again
_002: NOP 0
Hope this helps
The idea was to use the integrated clock (as it is stored on EEPROM and can be deleted only by software), but thanks anyway. Besides, I've been checking the SFC101 and it does not discard the minutes as it seemed