HI all,
I am facing a very strange problem at site,, there are two machines with same ip address which we are trying to connect with our scada. In order to avoid the IP conflict we have changed one of the machines and associated devices IP addresses to a different range to isolate the machine. But when we connect both machines in one network one of the running machine will show PLC fault and going to stop mode. Also we tried removing each devices and confirmed that this is happening only when both CPU's are in network. Any suggestions would be very much helpful.
Regards
Sandy
Compact PLC error
Re: Compact PLC error
Hi, have you checked the diagnostic buffer in order to know the reason why the plc is going to STOP mode?
This is a very helpful information to understand the problem.
This is a very helpful information to understand the problem.
-
- Posts: 32
- Joined: Thu Dec 18, 2014 4:52 pm
Re: Compact PLC error
Hi,
Machine manufacturer was checking the diag buffer and he couldnt see any ip conflict however I am at site today and will check the diag buffer and update you...
Regards
Sandeep
Machine manufacturer was checking the diag buffer and he couldnt see any ip conflict however I am at site today and will check the diag buffer and update you...
Regards
Sandeep
-
- Posts: 32
- Joined: Thu Dec 18, 2014 4:52 pm
Re: Compact PLC error
Hi,
I have checked the PLC fault table and could not see any major or minor faults. Also after monitoring the system we found that PLC is going to IO fault because of the festo controller is in fault mode. So whenever we connect both machines in one network either one of the festo controller will goes to fault mode and this makes the trouble.
Both festo CPX controller connected to the machine and we have seperated the IP address.
Regards
Sandeep
I have checked the PLC fault table and could not see any major or minor faults. Also after monitoring the system we found that PLC is going to IO fault because of the festo controller is in fault mode. So whenever we connect both machines in one network either one of the festo controller will goes to fault mode and this makes the trouble.
Both festo CPX controller connected to the machine and we have seperated the IP address.
Regards
Sandeep