[?]: How to crack password keyword stored in the SLC500 pro

RSLinx, RSLogix, RSView, LogixPro ...
Post Reply
Rogertecn
Posts: 78
Joined: Wed Nov 07, 2007 1:05 am
Location: UK

[?]: How unpassword master of Allen Bradley?

Post by Rogertecn » Tue Sep 16, 2008 1:23 am

Someone knows the password master of Allen Bradley to change programs that were created preventing changes?
I'm having problems.
Programs of RSlogix5 e 500.

most
Posts: 431
Joined: Sat Oct 22, 2005 7:17 am
Location: Europe

Post by most » Tue Sep 16, 2008 8:21 am


Rogertecn
Posts: 78
Joined: Wed Nov 07, 2007 1:05 am
Location: UK

NOT

Post by Rogertecn » Wed Sep 17, 2008 10:55 pm

It is not that. I mean that the password is to change programs after having been blocked.
HELP

nene
Posts: 51
Joined: Tue Sep 23, 2008 5:04 pm
Location: America

comlite32

Post by nene » Tue Oct 07, 2008 5:55 pm

not work for wimdows nt xp please post a program for work
windons xp very much

inupie
Posts: 16
Joined: Sun Aug 24, 2008 9:59 am
Location: Europe

Re: [?]: How unpassword master of Allen Bradley?

Post by inupie » Tue Oct 07, 2008 10:54 pm

Rogertecn wrote:Someone knows the password master of Allen Bradley to change programs that were created preventing changes?
I'm having problems.
Programs of RSlogix5 e 500.
As far as I remember (now just using Control Logix) the general password was 'abunlock'

Ryzhij
Posts: 404
Joined: Mon Mar 31, 2008 11:29 am
Location: Ryazan, Russia

Re: [?]: How unpassword master of Allen Bradley?

Post by Ryzhij » Wed Oct 08, 2008 7:11 am

I not sure at RSlogix500, but for RSlogix5 its true!
Then you aplay 'abunlock' you can open your file and will found the processor's 'name' (in it's properties).
This 'name' you can seek also then you have connect to PLC - "Hwo active?" function in RSLinx.
For reply/reset the password you can find 'name' in the hex-dump of theyour program file.
The next byte after processor's 'name' is the numer of symbol in password.
Examle: 0A hex - 10 next letters is the password.

Applied666
Posts: 8
Joined: Wed Oct 08, 2008 9:50 pm
Location: New Zealand

Post by Applied666 » Mon Jan 12, 2009 12:17 am

ABUNLOCK works great for SLC's and PLC5's, but not the microLOGIX range. Any idea of a password for this range?

Ryzhij
Posts: 404
Joined: Mon Mar 31, 2008 11:29 am
Location: Ryazan, Russia

Privilege Class-1 Password

Post by Ryzhij » Thu Oct 15, 2009 4:43 am

Are sambody know how to "repare" or reset the Privilege Class-1 Password for PLC-5 ?
Кто-нибудь знает как "восстановить" или сбросить пароль привилегий 1-го класса в PLC-5?

codientt
Posts: 18
Joined: Tue Aug 10, 2010 1:01 pm

[?]: How to crack password keyword stored in the SLC500 pro

Post by codientt » Thu Jan 13, 2011 2:14 pm

Dear All,
Help me link to download the software to remove keyword stored in the PLC program Rockwel.[
Now I have source programing. But I can't open it. Because it has passwords.
http://www.mediafire.com/?e78bi56z06n8hgi

Please help me to open it

Thanks and best regards

Eng_Ali
Posts: 35
Joined: Thu Jun 17, 2010 7:21 am

Re: [?]: How to crack password keyword stored in the SLC500

Post by Eng_Ali » Fri Jan 14, 2011 3:39 pm

Hello ,

use ( abunlock ) plz

(welc)

nene
Posts: 51
Joined: Tue Sep 23, 2008 5:04 pm
Location: America

Re: [?]: How to crack password keyword stored in the SLC500

Post by nene » Fri Jan 14, 2011 5:53 pm

hi
de password for file/code his 6114792
enjoy

codientt
Posts: 18
Joined: Tue Aug 10, 2010 1:01 pm

Re: [?]: How to crack password keyword stored in the SLC500

Post by codientt » Sat Jan 15, 2011 2:24 am

thank you very much.

Can you share with people how to crack Pro keyword in the program SLC500

Ryzhij
Posts: 404
Joined: Mon Mar 31, 2008 11:29 am
Location: Ryazan, Russia

Re: [?]: How to crack password keyword stored in the SLC500

Post by Ryzhij » Sat Jan 15, 2011 5:38 pm

codientt wrote:thank you very much.

Can you share with people how to crack Pro keyword in the program SLC500
Look to there viewtopic.php?f=12&t=13672 , but you need the %O ( not the %D ) to find in your HEX-dump.

michaeldanh
Posts: 2
Joined: Fri Feb 17, 2012 3:01 am

How to unsecure controller when it secured?

Post by michaeldanh » Tue Feb 28, 2012 3:51 am

I want upload project from CPU 1768 but it secured , i don't know password

fou99
Posts: 16
Joined: Tue Jul 20, 2010 1:23 pm

Re: How to unsecure controller when it secured?

Post by fou99 » Tue Feb 28, 2012 2:25 pm

Use wireshark . This software listen to all comunication on a ethernet card.

Open the programs, place a cross-wire with the PLC and check the communication. Go online, in all communication you should see the password

michaeldanh
Posts: 2
Joined: Fri Feb 17, 2012 3:01 am

Re: How to unsecure controller when it secured?

Post by michaeldanh » Fri Mar 02, 2012 8:32 am

I try use wireshark and can't see password?
I can online plc for upload and download
help me?you can instruction clearly?

hussein kamal
Posts: 39
Joined: Thu Jul 29, 2010 7:51 am

Re: How to unsecure controller when it secured?

Post by hussein kamal » Fri Mar 02, 2012 10:53 am

hi to you
fou99 can you tell me if you plz how i using program to get ip address of hmi and i don't have any data about it

fou99
Posts: 16
Joined: Tue Jul 20, 2010 1:23 pm

Re: How to unsecure controller when it secured?

Post by fou99 » Fri Mar 02, 2012 3:03 pm

http://plcplc.info/html/86/AB_RSLogix_5 ... ption.html

This is a example to unlock a SLC 500


For the HMI, just reboot the PanelView and click at the bottom left many until the HMI is boot. You will go to the configuration setup and you can see the IP address

alireza136110
Posts: 47
Joined: Wed Nov 26, 2008 8:01 am
Location: Iran

Re: [?]: How unpassword master of Allen Bradley?

Post by alireza136110 » Sun Oct 21, 2012 2:11 pm

hi every body. when i try to connect to AB plc the system wants to enter password, i use the universal password and micrologix connect to the plc but i cant monitor the block and software show me this program is protected. now i hove to know how i can take the safe backup and how i can modify programs.

thanks.

alireza136110
Posts: 47
Joined: Wed Nov 26, 2008 8:01 am
Location: Iran

Re: [?]: How to crack password keyword stored in the SLC500

Post by alireza136110 » Mon Oct 22, 2012 7:39 am

thanks for your attention.
my plc is SLC 5/05.

alireza136110
Posts: 47
Joined: Wed Nov 26, 2008 8:01 am
Location: Iran

Re: [?]: How to crack password keyword stored in the SLC500

Post by alireza136110 » Mon Oct 22, 2012 9:12 am

thanks.

cuongvcs
Posts: 145
Joined: Fri May 23, 2008 4:00 pm
Location: Vietnam

Re: [?]: How to crack password keyword stored in the SLC500

Post by cuongvcs » Mon Oct 22, 2012 6:04 pm

phanvantuan6 wrote:Try this http: http://www.4shared.com/rar/NC-KCC2G/AbKey.html
but you must register or have keygent.
Hi Tuan ,
Please help me ,how to use this software .
Thanks.

rhddev
Posts: 2
Joined: Wed Nov 28, 2012 4:59 am
Location: Brasil

Re: [?]: How to crack password keyword stored in the SLC500

Post by rhddev » Wed Nov 28, 2012 5:32 am

Hi, I'm new here, and first want to thanks you people for share the tools to our work. In return I wanto to share my private solution for this problem and for all the rslogix 500 compatibles plcs (tested for real with micrologix 1100,1200,1400 Serial and ethernet comms).

Now it's simple, after some hours debugging the rslogix I found some interesting things inside this software.

Number 1: You can just patch some bytes and bypass the password check to upload(plc->pc) a program. (My patch is for RSLogix 500 Version 8.10.00 (CPR 9) Build 18 [CRC32="67AF5288"]

Patch the file rs500.exe
Offset | Old Byte | New Byte
----------------------------------------
00313C64 | 74 | 90
00313C65 | 14 | 90
-----------------------------------------

We replace some instruction by nops and it's done. Save this file with a new name like, rs500_nopw.exe and try.
If a had some more time I'll try to port this patch to other versions of RSLogix.

Number 2: I also found a master password that I use to clear the protection. Go to the "Controller Properties" > "Passwords". PW 22865625 (erase any password).

If you just want to check if this method works, try to clear your own project's password with this number.

Thank everyon again. Cheers. (Sorry for my bad english, isn't my native language)

hhhjr
Posts: 5
Joined: Wed Apr 17, 2013 6:51 am

Re: [?]: How to crack password keyword stored in the SLC500

Post by hhhjr » Sat Apr 20, 2013 3:14 am

Hello, I have found the 2 bytes in hexedit, but it wont allow me to edit them. Is there a special way to edit them? Thanks Howard

hhhjr
Posts: 5
Joined: Wed Apr 17, 2013 6:51 am

Re: [?]: How to crack password keyword stored in the SLC500

Post by hhhjr » Sat Apr 20, 2013 9:42 pm

Thanks. I was able to upload the program. I edited it with hexedit.

Mark_Monitor
Posts: 5
Joined: Fri Jul 01, 2011 10:14 pm

Re: [?]: How to crack password keyword stored in the SLC500

Post by Mark_Monitor » Tue Apr 30, 2013 11:00 pm

rhddev wrote:Patch the file rs500.exe
Offset | Old Byte | New Byte
----------------------------------------
00313C64 | 74 | 90
00313C65 | 14 | 90
-----------------------------------------
*******
Great Work!
I have RS500 version 7.30.10 and I copied the executable to a separate folder, opened it with my hex editor. The line of code in this version for the bytes you mention above are as follows:
Offset: 00313C64 = 89
Offset: 00313C65 = 4D
I'm not sure if the password ignore parameter is a this byte address, and what the new values should be.
I am dealing with a dead beat OEM and our only option is build new equipment, but we really would like to start with the old code if possible. The code is in a Micrologix 1500.
Thanks for any advice,
Mark Monitor

*******

Mark_Monitor
Posts: 5
Joined: Fri Jul 01, 2011 10:14 pm

Re: [?]: How to crack password keyword stored in the SLC500

Post by Mark_Monitor » Thu May 02, 2013 5:49 pm


Thanks again rhddev!
I installed RSLogix 500 Version 8.10.00 and followed your instructions. This allowed me to upload the passworded code. Then I was able to use my hex editor and search for %D. This took me right to the existing password. I tested it with Micrologix 1000 and two Micrologix 1500's.
Great Job!
I'd like to do this with RSLogix Version 9 and RSLogix 5000- all versions.
MM

yeosh99
Posts: 59
Joined: Thu Jul 14, 2011 4:40 pm

Re: [?]: How to crack password keyword stored in the SLC500

Post by yeosh99 » Mon May 13, 2013 5:55 am

:?
Last edited by yeosh99 on Tue Dec 30, 2014 3:19 pm, edited 1 time in total.

yeosh99
Posts: 59
Joined: Thu Jul 14, 2011 4:40 pm

Re: [?]: How to crack password keyword stored in the SLC500

Post by yeosh99 » Wed May 15, 2013 8:36 am

(offtop) (offtop)
Last edited by yeosh99 on Tue Dec 30, 2014 3:29 pm, edited 1 time in total.

yeosh99
Posts: 59
Joined: Thu Jul 14, 2011 4:40 pm

Re: [?]: How to crack password keyword stored in the SLC500

Post by yeosh99 » Sun May 26, 2013 8:08 am

:?
Last edited by yeosh99 on Tue Dec 30, 2014 3:21 pm, edited 2 times in total.

Mark_Monitor
Posts: 5
Joined: Fri Jul 01, 2011 10:14 pm

Re: [?]: How to crack password keyword stored in the SLC500

Post by Mark_Monitor » Fri Jun 14, 2013 2:34 am

follow rhdev's instructions for v.8.10.00 this will ignore pw then hex edit search for %D which will highlight pw. exploring same option for v.9.0. tested on ml1200; ml1500

arfineira
Posts: 38
Joined: Wed Nov 12, 2008 1:30 pm
Location: America

Re: [?]: How to crack password keyword stored in the SLC500

Post by arfineira » Thu Feb 20, 2014 10:15 pm

Thank you for procedure rhdev´s, you save me...!! (clap)

Dear Mark_Monitor, can you to solve with RSLogix v9.0?

I don´t understand your explain.

best regards (pgood)

Mark_Monitor
Posts: 5
Joined: Fri Jul 01, 2011 10:14 pm

Re: [?]: How to crack password keyword stored in the SLC500

Post by Mark_Monitor » Mon Apr 07, 2014 2:37 pm

"Thank you for procedure rhdev´s, you save me...!! (clap)

Dear Mark_Monitor, can you to solve with RSLogix v9.0?

I don´t understand your explain.

best regards (pgood)"

I haven't solved the password bypass in version 9 yet...
mm

Yasir Maqsood
Posts: 22
Joined: Thu Jul 12, 2007 10:05 am
Location: Pakistan

Re: [?]: How to crack password keyword stored in the SLC500

Post by Yasir Maqsood » Fri Aug 22, 2014 5:54 pm

Hello Friends,
is there any success with Version 9....?

Faiz439
Posts: 1
Joined: Sun Dec 21, 2014 5:47 pm

Re: [?]: How to crack password keyword stored in the SLC500

Post by Faiz439 » Wed Aug 05, 2015 2:25 am

If anyone need help regard cracking of micrologix password in windows 7 contact me at faiz52uet@mail.com

rmaj4
Posts: 3
Joined: Mon Oct 26, 2015 2:29 pm

Re: [?]: How to crack password keyword stored in the SLC500

Post by rmaj4 » Mon Oct 26, 2015 2:45 pm

Hello everyone I 'am trying to get into a Micrologix 1500 and yes it is password protected. I saw some post describing a hex editor program that allows you to see the PW using %D command, if I 'am correct. I never used this hex editor before and would like to try it in my lab with a slc 500. After succeeding with the SLC 500 I'm hoping it will work with the Micro logix family of processors. Can anyone provide a procedure using Hex Editor to do this

psgama
Posts: 81
Joined: Thu Aug 08, 2013 6:00 pm

Re: [?]: How to crack password keyword stored in the SLC500

Post by psgama » Wed Oct 28, 2015 2:58 am

I don't see why it wouldn't work, as the password protection crack is done in the RSlogix500 software itself. You'll just have to find the same section of code in the version your using, so every version of Rslogix500 will have to have the instruction NOPed out

rmaj4
Posts: 3
Joined: Mon Oct 26, 2015 2:29 pm

Re: [?]: How to crack password keyword stored in the SLC500

Post by rmaj4 » Wed Oct 28, 2015 5:02 pm

Dont understand, what is NOPed. this my first time doing this.

psgama
Posts: 81
Joined: Thu Aug 08, 2013 6:00 pm

Re: [?]: How to crack password keyword stored in the SLC500

Post by psgama » Thu Oct 29, 2015 4:01 am

NOPing is changing an Assembly command from what it was to having no operation. So, that is what changing the 74 14 to 90 90 really means. 74 14 is a Jump equals short to a different address in the program after a test eax,eax is bening completed.

I just gave version 9.05.00 (CPR 9) a quick once over, but I don't have a micrologix or any SLC 500 processor to test anything on right now. Obviously, make yourself a backup of your rs500.exe , and test on a processor with your own project first.

I found 2 Short Jumps near the ABUNLOCK master password. In version 9.05.00 (CPR 9)

OFFSET 3566D3
74 14 Change to 90 90
Editing will skip offline file open password verification.
Last edited by psgama on Thu Oct 29, 2015 4:43 am, edited 1 time in total.

rmaj4
Posts: 3
Joined: Mon Oct 26, 2015 2:29 pm

Re: [?]: How to crack password keyword stored in the SLC500

Post by rmaj4 » Fri Oct 30, 2015 8:37 pm

Thank you that was a very good explanation, I my have some more questions but want to do some digging first.

psgama
Posts: 81
Joined: Thu Aug 08, 2013 6:00 pm

Re: [?]: How to crack password keyword stored in the SLC500

Post by psgama » Sat Oct 31, 2015 5:07 am

No problem. Making that change should allow you to download the password protected code, mind you I haven't tested it yet, I'm just assuming it will since it allowed me to view protected code without the password. You can save the project file, and then open it in a hex editor. You will then need to search for the processor name in the project. Or you can try to search for %D or %O Shortly after the processor name, you will find the password if it is not encrypted.

psgama
Posts: 81
Joined: Thu Aug 08, 2013 6:00 pm

Re: [?]: How to crack password keyword stored in the SLC500

Post by psgama » Tue Dec 22, 2015 10:41 pm

V10.00.00

Offset 3513AC
Change from 74 14 to 90 90 to accept any password

rohit02988
Posts: 8
Joined: Thu Aug 29, 2013 6:19 pm

Re: [?]: How to crack password keyword stored in the SLC500

Post by rohit02988 » Sun Feb 28, 2016 5:35 pm

rhddev

can you plz make for rslogix 500 version 8.10.00 (cpr8) build 24

i found below values on

00313c64 | 4d
00313c65 | a4

thanks waiting for your reply

rameshjsw
Posts: 1
Joined: Wed Dec 28, 2016 12:35 pm

How crack RSLOGIX 500

Post by rameshjsw » Wed Jan 04, 2017 6:35 pm

Dear Friends
Please help me friends i want learn rslogix 500 any one explain how to crack rslogix500

Regard
Ramesh Ganesan

Botswana

lukelukeluke
Posts: 1
Joined: Thu Oct 13, 2016 9:09 am

Re: [?]: How to crack password keyword stored in the SLC500

Post by lukelukeluke » Thu Dec 06, 2018 10:14 am

Hello
Do you know if this works with RSLogix 5000 also? There the exe is called "RSLogix5000Loader.exe"
Thanks

marildo
Posts: 2
Joined: Tue Feb 24, 2015 8:40 pm

Re: [?]: How to crack password keyword stored in the SLC500 pro

Post by marildo » Mon Jul 20, 2020 2:37 am

Hello!

Could someone help me find out the password for this program. The password has been encrypted.
Best regards

https://drive.google.com/file/d/1UkoohA ... sp=sharing

vlad2006gr
Posts: 1022
Joined: Tue Nov 20, 2007 7:08 pm
Location: Belarus

Re: [?]: How to crack password keyword stored in the SLC500 pro

Post by vlad2006gr » Mon Jul 20, 2020 1:48 pm

marildo wrote:
Mon Jul 20, 2020 2:37 am
Could someone help me find out the password for this program.
Link is not work

vlcampos
Posts: 1
Joined: Tue Dec 21, 2010 11:42 am

Re: [?]: How to crack password keyword stored in the SLC500

Post by vlcampos » Mon Nov 02, 2020 2:34 am

rmaj4 wrote:
Mon Oct 26, 2015 2:45 pm
Hello everyone I 'am trying to get into a Micrologix 1500 and yes it is password protected. I saw some post describing a hex editor program that allows you to see the PW using %D command, if I 'am correct. I never used this hex editor before and would like to try it in my lab with a slc 500. After succeeding with the SLC 500 I'm hoping it will work with the Micro logix family of processors. Can anyone provide a procedure using Hex Editor to do this
Use a USB sniffer program. The password is sent from the PLC to the PC (RSLogix Micro or 500) so it compares what you type to what is sent. The plc send it mixed with a lot of other data, but usually it is possible to identify the password.

Post Reply