Hi,
is it possible to configure two S7-400 CPU 414-2DP in one UR1 rack??
regards,
Ciwa
[?] : two CPU 414-2DP in one UR1 rack?
Re: [?] : two CPU 414-2DP in one UR1 rack?
try insert into hardware configuration
answer: no
answer: no
Re: [?] : two CPU 414-2DP in one UR1 rack?
Hi Sania,
In the hardware configuration, it's possible to insert two CPU 414-2DP.
But i don't know, it can download to both CPU or not.
regards,
Ciwa
In the hardware configuration, it's possible to insert two CPU 414-2DP.
But i don't know, it can download to both CPU or not.
regards,
Ciwa
Re: [?] : two CPU 414-2DP in one UR1 rack?
Run PLCSIM and view - impossible to upload to one CPU.ciwa wrote:In the hardware configuration, it's possible to insert two CPU 414-2DP.
But i don't know, it can download to both CPU or not.
This configuration is only for H-CPU.
Re: [?] : two CPU 414-2DP in one UR1 rack?
Possible. plcsim not real controller.