[?+]: OPC.SimaticNet - What's wrong?

ProTool, WinCC flexible, WinCC, PP/OP/TP/TD/MP
Post Reply
Timofei
Posts: 8
Joined: Thu Dec 06, 2007 6:25 am
Location: Russia

[?+]: OPC.SimaticNet - What's wrong?

Post by Timofei » Mon Oct 13, 2008 8:21 am

What I did:
1. SIMATIC Manager - created a project which increases value in DB1.DBD2 each X sec (CPU 315-2 DP).
- added PC station to a project (OPC server + CP5611)
- added PROFIBUS (Simatic station + PC station) in NetPro
Downloaded configuration to PLC.
2. Station configuration editor - added OPC server and CP5611(PROFIBUS)
3. SIMATIC NCM PC PC Station Wizard - Change local settings, Change hardware configuration.
4. HWConfig - Save and compile, Download to Module. After that status OPC server in Station Configuration Editor changed (no red cross on pensil).
5. OPC Scout - does not show me any actual data of DB1.DBD2.

What I did wrong?

Best regards.

marcs7
Posts: 52
Joined: Fri Jun 08, 2007 4:00 pm
Location: Europe

Post by marcs7 » Mon Oct 13, 2008 9:57 am

make a S7 liaison( from pc to cpu) in netpro
download liaison to simatic pc ..
enjoy

Timofei
Posts: 8
Joined: Thu Dec 06, 2007 6:25 am
Location: Russia

Post by Timofei » Mon Oct 13, 2008 11:31 am

Thanks a lot of.
It really helped me.