I created a Data type for the Face plate

then I created a Face-plate and created connection between the process value and the Data type tags

after this i crated another property called ShowHide_Faceplate (Bool) , then I set the objects on the Faceplate to hide when this Bit is 0 and become visible when this bit is 1

My problem is that when i use this Faceplate on the main screen and I create an invisible button on the top of the graphic so that on pressing it the Faceplate will Pop Up but to do so I need to conenct the Event setting of this invisible button to this tag ShowHide_Faceplate but this tag is not showing in the tag list of HMI and I am unable to connect the invisible button to Faceplate

https://imgur.com/gallery/iIHt0Gw
Image

stoprun
Posts: 10
Joined: Sun Apr 04, 2010 7:36 pm

Re: [?]: WinCC Flexible Faceplate

Post by stoprun » Mon Oct 21, 2019 8:00 am

First, always check if "Hmi/OPC/UA" check box is checked in your PLC DB.
So?

ggg315
Posts: 26
Joined: Thu May 28, 2015 6:29 am

Re: [?]: WinCC Flexible Faceplate

Post by ggg315 » Mon Oct 21, 2019 3:06 pm

i was able to fix this problem by making a HMI tag Internal type and then connecting this tag to the Button Even and also in faceplate properties this tag was connected to the BIT