Communication between Schneider HMIGTO2300 and TWDLCAA10DRF

другие контроллеры
tewatute
Posts: 1
Joined: Mon Jan 13, 2014 5:51 pm

Communication between Schneider HMIGTO2300 and TWDLCAA10DRF

Post by tewatute » Mon Mar 17, 2014 5:14 am

Hello,

i need some help!!

i connected both via rs-485 by lan cable.

HMI PLC

RJ-45 Mini Din 8 pin

pin4 A <---> pin1 A

pin5 B <---> pin2 B

pin8 SG <---> pin7 0V

PLC : I config in Twidosuite(Descrobe) to 19200 8 E 1 tried other baud rate too.

HMI : I config in IO Manager --> ModbusRTU01[Com2] to 19200 8 E 1 and ModbusEquipment1 to address 1(PLC)

but when i power on i get msg on HMI display "No reply from PLC within Timeout period. (ModbusEquipment01)"

i need config more? i missed something?

please help!!! or give some instruction.

Thank you.

luke12faulin
Posts: 27
Joined: Wed Mar 11, 2009 1:35 am

Re: Communication between Schneider HMIGTO2300 and TWDLCAA10

Post by luke12faulin » Thu Mar 20, 2014 7:56 am

tewatute,

Herewith the configuration of Both..

PLC TWDLCAA10DRF

1. Using Twido Suite, at the Describe Toolbar, put by drag and drop PLC (Base->Compact->TWDLCAA10DRF) and HMI (Network Elements->Modbus Elements->Magelis)

2. Connected point to point PLC and Network Element
3. Configuration setting:
a.
Network Elements
Name = any
Type = Modbus
Address = Master
b.
Network
Type = No Change
Name = any
Baudrate = 19200
Data Bits = 8 (RTU)
Parity = none
Stop Bit = 1
Timeout = 10 x 100ms
Time between frames (ms) = 10 ms

c.
Twido PLC Port 1:
Type = No Change
Address = 1 (Should be same as the HMI)

HMI Vijeo Designer

IO Manager, selected:
a.
Manufacturer = Schneider Electric Industries SAS
Driver = Modbus (RTU)
COM Port = COM1
Serial Interface = no change
Flow Control = no change
Transmission Speed = 19200
Parity Bit = None
Stop Bit = 1

b.
Equipment Configuration = Modbus Equipment
Slave Equipment Address = 1
Comm. Optimization = Custom, 120 bytes
IEC61131 Syntax = "Check"
Addressing Mode = 0-based (Default)
Variables = Double Word word order (Low word first), ASCII Display byte order (Low byte first)


Cable Connection, RS-485
HMI [COM 1, RJ45], Twido MiniDIN 8 [PORT 1]

HMI [4] --------------------- [1] MiniDIN (+)
HMI [5] --------------------- [2] MiniDIN (-)

BR