[?]:alarm list configuration 800xA 5.1 control builder M pro

другие контроллеры
Post Reply
azgor_03
Posts: 27
Joined: Mon Dec 30, 2013 5:23 am

[?]:alarm list configuration 800xA 5.1 control builder M pro

Post by azgor_03 » Mon Jan 06, 2014 12:06 pm

i am not getting alarm & event in operator work place. what should do
pls sen a procudure

Linkinx64
Posts: 894
Joined: Sun Apr 11, 2010 3:00 am
Location: Russia

Re: alarm list configuration 800xA 5.1 control builder M pro

Post by Linkinx64 » Mon Jan 06, 2014 6:50 pm

There are 2 kind of alarms in 800xA system: soft alarms (800xA services status) and process alarms (hardware state). Which one you not getting?
Do you see an yellow rectangle surrounding the alarm list perimeter?
Did you connect Alarm & Event on the 2nd tab of AC 800M OPC Control Panel?

azgor_03
Posts: 27
Joined: Mon Dec 30, 2013 5:23 am

Re: alarm list configuration 800xA 5.1 control builder M pro

Post by azgor_03 » Tue Jan 07, 2014 2:36 am

not getting process alarm

Linkinx64
Posts: 894
Joined: Sun Apr 11, 2010 3:00 am
Location: Russia

Re: alarm list configuration 800xA 5.1 control builder M pro

Post by Linkinx64 » Tue Jan 07, 2014 9:58 am

Create "Process alarm" service group under "Event collector" service. Then create a service provider for this group and assign it to the node where ABB AC 800M OPC Server is running. After that go back to the service group and assign "OPC A&E Server..." (not remember clearly) as an "Alarm Server" and upload data.

azgor_03
Posts: 27
Joined: Mon Dec 30, 2013 5:23 am

Re: alarm list configuration 800xA 5.1 control builder M pro

Post by azgor_03 » Tue Jan 07, 2014 12:05 pm

Suppose i have a hardware input like H212DR03VS10AV ( travel vfd-1 availability) what will be input pin for AlarmCond block.
1. signal
2. ScrName
3. Message

Linkinx64
Posts: 894
Joined: Sun Apr 11, 2010 3:00 am
Location: Russia

Re: alarm list configuration 800xA 5.1 control builder M pro

Post by Linkinx64 » Tue Jan 07, 2014 2:32 pm

azgor_03 wrote:Suppose i have a hardware input like H212DR03VS10AV ( travel vfd-1 availability) what will be input pin for AlarmCond block.
1. signal
2. ScrName
3. Message
Signal - input to activate alarm (e.g. H212DR03VS10AV.Value)
SrcName - alarm source object (e.g. Reactor). Shouldn't exceed 15 characters or contain spaces, dots, etc.
Message - message to be shown to the operator (e.g. "Inlet valve opened.")

azgor_03
Posts: 27
Joined: Mon Dec 30, 2013 5:23 am

Re: alarm list configuration 800xA 5.1 control builder M pro

Post by azgor_03 » Wed Jan 08, 2014 2:28 am

when i am going to new aspect/ object under event collector like process alarm but getting process object configuration & process object locking. what should be the next.

azgor_03
Posts: 27
Joined: Mon Dec 30, 2013 5:23 am

Re: alarm list configuration 800xA 5.1 control builder M pro

Post by azgor_03 » Wed Jan 08, 2014 8:51 am

after connecting, i am not able to upload. it showing no contact with server
setting:
1. Alarm server:
OPC AE Server for AC 800M
2. Collection Definition:
OPC AE Server for AC 800M
3. Object handelier:
Traking Source object interceptor
4. Source configuration:
OPC AE Server for AC 800M: Source object interceptor
what could be the next

azgor_03
Posts: 27
Joined: Mon Dec 30, 2013 5:23 am

Re: [?]:alarm list configuration 800xA 5.1 control builder M

Post by azgor_03 » Thu Jan 09, 2014 3:20 am

After changing
3. Object handelier:
Traking Source object interceptor
to
Default source object, it has uploaded. Now i am facing one problem that the Event collector service become yellow(synchronizing) in PPA

Also the OPCADA connector become yellow ( Initialize) in PPA.
Please give suggestion

Linkinx64
Posts: 894
Joined: Sun Apr 11, 2010 3:00 am
Location: Russia

Re: [?]:alarm list configuration 800xA 5.1 control builder M

Post by Linkinx64 » Sat Jan 11, 2014 9:28 am

Who did said to change an "Object Handler" section setting?
After selection of the "alarm server" as OPC AE Server for AC 800M the other settings on this aspect remains default.
The only was needed to select the node for the service provider (computer where OPC server is running).

azgor_03
Posts: 27
Joined: Mon Dec 30, 2013 5:23 am

Re: [?]:alarm list configuration 800xA 5.1 control builder M

Post by azgor_03 » Sun Jan 12, 2014 2:40 am

Now i am facing one problem that the Event collector service become yellow(synchronizing) in PPA

Also the OPCADA connector become yellow ( Initialize) in PPA.
Please give suggestion

Linkinx64
Posts: 894
Joined: Sun Apr 11, 2010 3:00 am
Location: Russia

Re: [?]:alarm list configuration 800xA 5.1 control builder M

Post by Linkinx64 » Sun Jan 12, 2014 8:34 am

I suggest to delete newly created "Process Alarms" service group, restart the aspect server and try create this group from the beginning , without changes of the object handler.

Post Reply