[?]:alarm list configuration 800xA 5.1 control builder M pro

Posted: Mon Jan 06, 2014 12:06 pm
by azgor_03
i am not getting alarm & event in operator work place. what should do
pls sen a procudure

Re: alarm list configuration 800xA 5.1 control builder M pro

Posted: Mon Jan 06, 2014 6:50 pm
by Linkinx64
There are 2 kind of alarms in 800xA system: soft alarms (800xA services status) and process alarms (hardware state). Which one you not getting?
Do you see an yellow rectangle surrounding the alarm list perimeter?
Did you connect Alarm & Event on the 2nd tab of AC 800M OPC Control Panel?

Re: alarm list configuration 800xA 5.1 control builder M pro

Posted: Tue Jan 07, 2014 2:36 am
by azgor_03
not getting process alarm

Re: alarm list configuration 800xA 5.1 control builder M pro

Posted: Tue Jan 07, 2014 9:58 am
by Linkinx64
Create "Process alarm" service group under "Event collector" service. Then create a service provider for this group and assign it to the node where ABB AC 800M OPC Server is running. After that go back to the service group and assign "OPC A&E Server..." (not remember clearly) as an "Alarm Server" and upload data.

Re: alarm list configuration 800xA 5.1 control builder M pro

Posted: Tue Jan 07, 2014 12:05 pm
by azgor_03
Suppose i have a hardware input like H212DR03VS10AV ( travel vfd-1 availability) what will be input pin for AlarmCond block.
1. signal
2. ScrName
3. Message

Re: alarm list configuration 800xA 5.1 control builder M pro

Posted: Tue Jan 07, 2014 2:32 pm
by Linkinx64
azgor_03 wrote:Suppose i have a hardware input like H212DR03VS10AV ( travel vfd-1 availability) what will be input pin for AlarmCond block.
1. signal
2. ScrName
3. Message
Signal - input to activate alarm (e.g. H212DR03VS10AV.Value)
SrcName - alarm source object (e.g. Reactor). Shouldn't exceed 15 characters or contain spaces, dots, etc.
Message - message to be shown to the operator (e.g. "Inlet valve opened.")

Re: alarm list configuration 800xA 5.1 control builder M pro

Posted: Wed Jan 08, 2014 2:28 am
by azgor_03
when i am going to new aspect/ object under event collector like process alarm but getting process object configuration & process object locking. what should be the next.

Re: alarm list configuration 800xA 5.1 control builder M pro

Posted: Wed Jan 08, 2014 8:51 am
by azgor_03
after connecting, i am not able to upload. it showing no contact with server
setting:
1. Alarm server:
OPC AE Server for AC 800M
2. Collection Definition:
OPC AE Server for AC 800M
3. Object handelier:
Traking Source object interceptor
4. Source configuration:
OPC AE Server for AC 800M: Source object interceptor
what could be the next

Re: [?]:alarm list configuration 800xA 5.1 control builder M

Posted: Thu Jan 09, 2014 3:20 am
by azgor_03
After changing
3. Object handelier:
Traking Source object interceptor
to
Default source object, it has uploaded. Now i am facing one problem that the Event collector service become yellow(synchronizing) in PPA

Also the OPCADA connector become yellow ( Initialize) in PPA.
Please give suggestion

Re: [?]:alarm list configuration 800xA 5.1 control builder M

Posted: Sat Jan 11, 2014 9:28 am
by Linkinx64
Who did said to change an "Object Handler" section setting?
After selection of the "alarm server" as OPC AE Server for AC 800M the other settings on this aspect remains default.
The only was needed to select the node for the service provider (computer where OPC server is running).

Re: [?]:alarm list configuration 800xA 5.1 control builder M

Posted: Sun Jan 12, 2014 2:40 am
by azgor_03
Now i am facing one problem that the Event collector service become yellow(synchronizing) in PPA

Also the OPCADA connector become yellow ( Initialize) in PPA.
Please give suggestion

Re: [?]:alarm list configuration 800xA 5.1 control builder M

Posted: Sun Jan 12, 2014 8:34 am
by Linkinx64
I suggest to delete newly created "Process Alarms" service group, restart the aspect server and try create this group from the beginning , without changes of the object handler.