[?+]: PLC TSX Quantum CPU 113/30

другие контроллеры
kresekjoy
Posts: 25
Joined: Sat Apr 30, 2011 6:44 am
Location: Indonesia

[?+]: PLC TSX Quantum CPU 113/30

Post by kresekjoy » Sat Jun 25, 2011 4:04 am

Hi all, I newbi on Schneider PLC (nuser)

I need a wiring schematic download / upload TSX Quantum cpu 113/30
1. Is it possible to directly use the rs 232 serial cable direct to pc / laptop?
2. In Which port for program upload / download on this cpu? Modbus or Modbus Plus?
3. Are there any specific setting in order to Connect? Exp. Baudrate, parity or data bits?
4. Can I use Proworx? NXT or Proworx32?

Thank for your assistance all

(tyou) (tyou)

leofarhan
Posts: 122
Joined: Fri May 01, 2009 8:50 am

Re: Need Help..PLC TSX Quantum CPU 113/30

Post by leofarhan » Sat Jun 25, 2011 6:55 am

Hello Dear,

The link contains the details of 140CPU11303 http://www.filesonic.com/file/130217547 ... inouts.pdf
on the last two pages you can find the connection diagram.

1. Yes, you can download program via RS232 port of you laptop/PC.
2. You can download program via both ModBus & ModBus Plus port, but for ModBus plus you need ModBus Plus card. It is better you download program via ModBus Port, although it is a bit slow, but it does not required additional hardware to download.
3. The Software automatically scan the ModBus address, baud rate & parity, you don't need to configure it.
4. Yes, You can you ProWorx Software.

BR
Leo-Ali

kresekjoy
Posts: 25
Joined: Sat Apr 30, 2011 6:44 am
Location: Indonesia

Re: [?]: PLC TSX Quantum CPU 113/30

Post by kresekjoy » Sat Jun 25, 2011 3:21 pm

Yup,

Your answer all is working and I've tried it

Thank you profusely

Case closed