Hi all
anybody have a sch on cable for connect PC to Siemens Micromaster inverter (for upload a parameters) I have a OP, but this is very lazy work thanks!
[?]: cable to upload parameters on Micromaster
-
- Posts: 4
- Joined: Sat Sep 12, 2009 6:39 am
- Location: Europe
Hello,
You have to Purchase a PC inverter kit (6SE6400-1PC00-0AA0) to use RS232 port of drive, or you can use terminal 29 and 30 on I/O module But then you will required a RS 485 to RS 232 converter.
Look at https://www.automation.siemens.com/WW/f ... anguage=en .
This converter also protect your PC from possible damage.
Hope this will helps.
Regards
You have to Purchase a PC inverter kit (6SE6400-1PC00-0AA0) to use RS232 port of drive, or you can use terminal 29 and 30 on I/O module But then you will required a RS 485 to RS 232 converter.
Look at https://www.automation.siemens.com/WW/f ... anguage=en .
This converter also protect your PC from possible damage.
Hope this will helps.
Regards
-
- Posts: 4
- Joined: Sat Sep 12, 2009 6:39 am
- Location: Europe
I find this sch for RS 485 to RS 232:
http://aquaticus.info/files/RS485%20to% ... ematic.png
This week i will make this and report result
http://aquaticus.info/files/RS485%20to% ... ematic.png
This week i will make this and report result
What is the voltage Vcc?Luca_Brasi wrote:I find this sch for RS 485 to RS 232:
http://aquaticus.info/files/RS485%20to% ... ematic.png
This week i will make this and report result
regard
7805 = 5 Vcrack_x01 wrote: What is the voltage Vcc?
regard
about rs232/485
some projects and link in http://www.edaboard.com/ftopic71311.html
(need register)
Re: [?]: cable to upload parameters on Micromaster
I'm using this: