PostPosted: Mon Oct 16, 2017 11:09 am 

Joined: Mon Dec 14, 2015 8:45 am
Posts: 36
AFTER DEAD MEAN PLATE IN FREQUENCE DRIVER WE ARE SETUP NEW PLATE.
THEN WE TRY TO CHANGE PARAMETR CURRENT TO 200A WE HAVE NOT CAN CHANGE BECOUSE PROGRAMM GIVED MESSAGE:
- Modbus device returned an exception code 3 (ILLEGAL DATA VALUE: A value contained in the query data field is not an allowable value for the slave.

Perhaps Value outside min--max limits,
Parameter is read-only,
Parameter write not allowed when Drive is running or
Parameter write not allowed when factory macro is selected.
Also check that parameter lock-parameter is not active) while writing register 101
(THEN WE TRY TO CHANGE 18A - OK..20-OK 21- NOK)
WHAT WE MUST DO TO SOLVE THE LIMIT?


Top
 Profile  
 
PostPosted: Mon Oct 16, 2017 1:12 pm 

Joined: Mon Dec 14, 2015 8:45 am
Posts: 36
zaplatin wrote:
AFTER DEAD MEAN PLATE IN FREQUENCE DRIVER WE ARE SETUP NEW PLATE.
THEN WE TRY TO CHANGE PARAMETR CURRENT TO 200A WE HAVE NOT CAN CHANGE BECOUSE PROGRAMM GIVED MESSAGE:
- Modbus device returned an exception code 3 (ILLEGAL DATA VALUE: A value contained in the query data field is not an allowable value for the slave.

Perhaps Value outside min--max limits,
Parameter is read-only,
Parameter write not allowed when Drive is running or
Parameter write not allowed when factory macro is selected.
Also check that parameter lock-parameter is not active) while writing register 101
(THEN WE TRY TO CHANGE 18A - OK..20-OK 21- NOK)
WHAT WE MUST DO TO SOLVE THE LIMIT?


на плате был выбран тип привода dcs401 соответственно ток у него 20А макс.
C ПУЛЬТА ДЛЯ ПРИВОДА ВЫБИРАЕМ:
MENU-LONG/SHORT-LONG-SET TYPE CODE - 400 (ПАРОЛЬ ИЗ ИНСТРУКЦИИ) - ВЫБИРАЕМ ТИП ДРУГОЙ DCS402.0680 ПЕРЕЗАГРУЖАЕМ ПРИВОД .
ПОСЛЕ ЭТОГО ЛИМИТ ТОКА 1000А


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC + 3 hours


Who is online

Users browsing this forum: No registered users and 3 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum

Search for:
Jump to:  
Powered by International PLCforum® Forum Software © PLCforum
Mobile version