Hi every body,
I have a big problem with CitectSCADA and SIMATIC Net.
I must communicate between Citect and about 20 SIEMENS PLCs ( S7-300 and S7-400), so i follow instructions and create connections. every thing is good until eleventh connection. Citect can't communicate more than ten Siemens PLC.
Now, i want know:
1- Is there any limit on the number of connections between Citect and Siemens PLCs (or between Simatic Net and Siemens PLCs)?
2- If "YES", What can i do?
Additional notes: I use CitectSCADA version 7.2 SP1 Demo license and SIMATIC Net version 5.4 full license.
Best regards
[HELP] CitectSCADA S7NT Driver limitation?
Re: [HELP] CitectSCADA S7NT Driver limitation?
CitectSCADA Knowladgebase. Q3784 Configuring CitectSCADA Projects for Optimal Communication to Siemens S7 PLCs Using the S7 Driver: "...The Siemens Softnet V6 only allows a maximum of 10 connections or "channels" for external applications such as Citect. It can however support up to 64 Devices/PLC's to be shared among these 10 connections. If you require more than 64 PLC's on a single I/O Server, you can alternatively use the PSDIRECT driver."