1794-IE12 module remains flashing after configured

RSLinx, RSLogix, RSView, LogixPro ...
Post Reply
Satronic
Posts: 1
Joined: Tue May 12, 2020 5:37 pm

1794-IE12 module remains flashing after configured

Post by Satronic » Tue May 12, 2020 5:39 pm

I have a doubt, I'm configuring a 1794-IE12 module using the 1794-TB3G base, using a 1794-ADN with 1756-DNB, the LEDs on the 1756 and 1794-ADN card are OK, but the 1794-IE12 module led flashes green.

pogo-1
Posts: 4
Joined: Sat Jul 07, 2012 9:54 am

Re: 1794-IE12 module remains flashing after configured

Post by pogo-1 » Fri Jun 26, 2020 1:57 am

When used in a Logix5000 system, verify the Adapter:Slot:O.OutputEnable bit is set to 1

https://literature.rockwellautomation.c ... _-en-p.pdf