[?]: Allen bradley MSG

RSLinx, RSLogix, RSView, LogixPro ...
Post Reply
omar zedan
Posts: 237
Joined: Sat Oct 22, 2011 7:12 am

[?]: Allen bradley MSG

Post by omar zedan » Sat Sep 22, 2012 5:30 pm

Dear All
I use compactlogix L35E with IP(192.168.1.6)
With FlexLogix L34 with daughtercard with IP(192.168.1.2)
I need to read info. from flexlogix therefore I use MSG

Code: Select all

 Config. Tab is CIP Data Table Read and (Source element ..... Nu. of ele........Desti......)
Commun. Tab is (LocalENB,2,192.168.1.2)
But an error happens 16#0004, what should I do?
Thanks

omar zedan
Posts: 237
Joined: Sat Oct 22, 2011 7:12 am

Re: [?]: Allen bradley MSG

Post by omar zedan » Mon Sep 24, 2012 9:27 am

Dear All
the communication path should be
LocalENB(the name of ethernet port in compact logix),2(ethernet symbol),192.168.1.2 (the flexlogix ethernet daughtercard IP"the distination IP"),1(the number 1 means to backplane),0 (the Slot number of the flexlogix CPU"Destination")
Thanks