[?]: how connect panel view C600 with micrologix 1100 ?
-
- Posts: 36
- Joined: Sun Sep 04, 2011 10:58 pm
[?]: how connect panel view C600 with micrologix 1100 ?
I need to connect panel view C600 with micrologix 1100 but HMI didn't connect and i need to know how i can make it
Re: [?]: how connect panel view C600 with micrologix 1100 ?
Let me know catalog numbers your equipment - panel view C600 and micrologix 1100.
-
- Posts: 36
- Joined: Sun Sep 04, 2011 10:58 pm
Re: [?]: how connect panel view C600 with micrologix 1100 ?
panel view C600 cat. No. 2711C-T6M Ser. C Rev. ARyzhij wrote:Let me know catalog numbers your equipment - panel view C600 and micrologix 1100.
Micrologix 1100 Cat. No. 1763-L16BBB Ser. B Rev. E
PLC program http://www.4shared.com/file/RDduoIVw/UP ... P-PLC.html
HMI program http://www.4shared.com/file/QBvoUgUE/UP00067-HMI.html
Re: [?]: how connect panel view C600 with micrologix 1100 ?
First of all, you mast to setup channels into your micrologix 1100 programm.
And to do same for panel.( Your application UP00067-HMI is secured. Do you know the Login & Password for Designer right? )
Good luck!
And to do same for panel.( Your application UP00067-HMI is secured. Do you know the Login & Password for Designer right? )
Good luck!
-
- Posts: 36
- Joined: Sun Sep 04, 2011 10:58 pm
Re: [?]: how connect panel view C600 with micrologix 1100 ?
i sent password and user name in PM to you and how i can setup channels in micrologix 1100 program & panelRyzhij wrote:First of all, you mast to setup channels into your micrologix 1100 programm.
And to do same for panel.( Your application UP00067-HMI is secured. Do you know the Login & Password for Designer right? )
Good luck!
Re: [?]: how connect panel view C600 with micrologix 1100 ?
First of all, it should be noted that the direct link between the panel PVc-C600 and controller MicroLogix-1100 is only possible via the serial interface.
See pages 60-61 of PanelView Component HMI Terminals User Manual 2711C-UM001F-EN-P
Usually use RS232 DF1 protocol via cable 1761-CBL-PM02 (see there page 63).
I found it in your projects for the panel (and to the controller too) no serial port settings. This should be done.
Apply for this program RSLogix500 + RSLinx and PanelView_Component_DesignStation.
You also need to install the controller the same name in both projects.
I hope this file Screenshots.zip with illustrations to help you.
Ethernet is used to connect the computer with the configuration of devices and for SCADA/DCS. About how to configure the Ethernet on pages 221-228 of MicroLogix 1100 Programmable Controllers User Manual 1763-UM001D-EN-P and also on pages 44-47 of PanelView Component HMI Terminals User Manual 2711C-UM001F-EN-P
Good luck!
See pages 60-61 of PanelView Component HMI Terminals User Manual 2711C-UM001F-EN-P
Usually use RS232 DF1 protocol via cable 1761-CBL-PM02 (see there page 63).
I found it in your projects for the panel (and to the controller too) no serial port settings. This should be done.
Apply for this program RSLogix500 + RSLinx and PanelView_Component_DesignStation.
You also need to install the controller the same name in both projects.
I hope this file Screenshots.zip with illustrations to help you.
Ethernet is used to connect the computer with the configuration of devices and for SCADA/DCS. About how to configure the Ethernet on pages 221-228 of MicroLogix 1100 Programmable Controllers User Manual 1763-UM001D-EN-P and also on pages 44-47 of PanelView Component HMI Terminals User Manual 2711C-UM001F-EN-P
Good luck!