Hi,
I have a problem scheduling my CNET network. The CPU runs on Controllogix v13.XX.
I use the RSNetworx for ControlNet V 9.00.
The actual configuration have one communication adapter 1756-CNB/D (node 01), 3 flex chasis with 1794-ACN15/C whith rev 4.1 (nodes 2 to 4), Panelview 600 standard (node 05).
The two new ones I added, 1794-ACN15/C (nodes 6 & 7) has Major rev. 4 and minor Rev 3.
The problem is when I pick on line at RsNetworx program this begin scanning the network, but no complete the graphical representation of the network, only appears all ACN15 ControlNet adapters (nodes 2 to 4 and 6 &7), panel view (node 5), but the node 01 (1756-CNB/D) is not showing.
The RsNetworx continuous browsing the network but never stop.
Any Idea?
Thanks a lot!
[?]: ControNet problem
Re: ControNet problem
Hi,
Do you use network adaptator to browse your ControlNet Network?
If Yes , chek his adress : keep sure there is no duplicate node!!
Best regards
Do you use network adaptator to browse your ControlNet Network?
If Yes , chek his adress : keep sure there is no duplicate node!!
Best regards
Re: [?]: ControNet problem
Thanks dehell but I connect to PLC via 1756 ENBT/A
Best regards
jramos354
Best regards
jramos354
Re: [?]: ControNet problem
update the file EDS for PV600 and 1756-CNB/D
Re: [?]: ControNet problem
IMHO you must update F/W revision your 1794-ACN15/C (nodes 6 & 7) to same rev 4.1 (nodes 2 to 4).
Re: [?]: ControNet problem
could u try connect pc to plc via RS232