Hello dear all , I need to drive few inverter Danfoss vlt2800 with a cpu 315-2DP via profibus .
Anyone have an example FC or FB ?

any help is appreciated !

Thanks

dsekulic
Posts: 186
Joined: Sun Feb 12, 2006 5:47 pm
Location: Europe

Post by dsekulic » Tue Dec 16, 2008 11:06 am

Hi,

You just need GSD file from vlt2800 and import them in hardware configuration.
Than parametrize vlt2800 instance in HWconfig and download to S7-300.
All input data You should see in PII (from HWconfig) and commands are writed in PIQ (from HWconfig).
That's all.
Also if vlt2800 support DPV1 than You can communicate asynchronicaly with inverter.
http://www.pribor-servis.ru/downloads/d ... 90E102.pdf

GSD and example
http://www.danfoss.com/businessareas/dr ... +files.htm
regards

dibolo
Posts: 74
Joined: Fri Mar 03, 2006 10:18 am
Location: Europe

Post by dibolo » Tue Dec 16, 2008 3:39 pm


sania
Site Admin
Posts: 1371
Joined: Sat Aug 13, 2005 6:15 am
Contact:

Post by sania » Tue Dec 16, 2008 4:05 pm

if you want,you can try it