Dear All
I have CPU 319 CPU connected to 3 Danfoss drive via profinet
(I connect my laptop to the hab and I found the PLC and the 3 Danfoss "the network is good"),
the BF3 flashing red and the diag. buffer
(IO access error writing P area, word access, Access address 2602 Request OB I/O access error OB (OB122), Priority class 1 External error, Incoming event)
the address 2602 dose not exist in hardware, also the OB122 used.
What can I do to solve this issue?
Thanks
-
georg_demmler
- Posts: 71
- Joined: Wed Nov 18, 2009 4:02 pm
Post
by georg_demmler » Fri Aug 12, 2022 6:35 am
Hello,
what do you expected from the forum ?
That we guess what happens - please put some pictures about the online Hardwareconfiguration so we see the hardware.
What is the Event-ID of the diag. buffer? Is the equipment old or new.
How did you check "network is good".
We need a little bit more information if you want help from the forum.
In German we have a slang - here you have a bone look for the meat.
Thanks
-
CoMod
- Site Admin
- Posts: 3977
- Joined: Thu Feb 16, 2006 3:25 pm
- Location: Russia
Post
by CoMod » Sun Aug 14, 2022 10:08 am
See Cross-reference table - PIW/PQW 2602 is used in FC91
-
omar zedan
- Posts: 237
- Joined: Sat Oct 22, 2011 7:12 am
Post
by omar zedan » Sun Aug 14, 2022 12:38 pm
Yes, sir, I find this address (also there is PQW 2602), and when I try to use it in a variable table the status field in the variable table shows me nothing just a glass icon with a line inside it.
maybe something out of range? I don't know.
What is the glass icon inside the variable table (Status field)?
and how can I solve this issue?
Thanks
-
CoMod
- Site Admin
- Posts: 3977
- Joined: Thu Feb 16, 2006 3:25 pm
- Location: Russia
Post
by CoMod » Sun Aug 14, 2022 1:30 pm
this program downloaded from PLC
no symbol names
no comments
For decision need full source of Step7 project with symbol names and comments
and documentation with schemes
эта программа скачана с ПЛК
нет названий, символьных имён
без комментариев
Для решения нужен полный исходник проекта Step7 с именами символов и комментариями
и документация со схемами
-
sania
- Site Admin
- Posts: 1371
- Joined: Sat Aug 13, 2005 6:15 am
Post
by sania » Mon Aug 15, 2022 2:29 pm
это пустышка,
сотри букву Р , так и прогу не меняешь и лампочку погасишь
delete "P" in "PIW" / "PQW" it will not change program and correct the error
-
georg_demmler
- Posts: 71
- Joined: Wed Nov 18, 2009 4:02 pm
Post
by georg_demmler » Tue Aug 16, 2022 11:17 am
Hello,
this is my only comment - it is nice to get a program without any symbolic.
So here is what I find - yes the program use the address 2602
Go to the hardware - select the part with the CPU 319 and on the slot X3 you find the CPU-CA140-1. Select this and you find the I-Device the address range
for inputs / outputs from 2600-2663.
But I don't know how its works.
Hope this helps
-
omar zedan
- Posts: 237
- Joined: Sat Oct 22, 2011 7:12 am
Post
by omar zedan » Tue Aug 16, 2022 8:15 pm
Thanks a lot, friends.
-
georg_demmler
- Posts: 71
- Joined: Wed Nov 18, 2009 4:02 pm
Post
by georg_demmler » Wed Aug 17, 2022 5:30 am
Hello,
some information about your plc.
The program what you send is a I-device - that means you have a master and one (or more) I-devices.
The communication between the I-device and the master is over inputs and outputs.
You definied in the I-device the Inputrange and Outputrange - create a GSD-File and put this GSD-File in the Master-PLC.
You find a very helpful video in YT - Siemens SIMATIC Manager_Communication between two PLC Using I Device option (S7-300/S7-400)
And the read BF light shows, that the Master-PLC is missing.
KHS is a german company and let me guess - the program is working in a liquid area (filling and so on)
Hope this helps.
-
omar zedan
- Posts: 237
- Joined: Sat Oct 22, 2011 7:12 am
Post
by omar zedan » Fri Sep 02, 2022 7:58 pm
Thanks, Friend
You are right