[?]: 24vac PLC inputs ?

Post by Jbeard » Mon Jun 22, 2020 12:54 pm

I know that most PLC inputs are 24vdc,
but what would happen to the PLC if you applied 24vac to the inputs if it was a dc input?

misa1515
Posts: 53
Joined: Mon Jan 03, 2011 10:51 am

Re: PLC inputs

Post by misa1515 » Mon Jun 22, 2020 3:35 pm

Hello,
24VAC on 24VDC input - value in PLC will flicker on 0 and 1

Jbeard
Posts: 22
Joined: Fri Jun 28, 2019 1:08 am

Re: PLC inputs

Post by Jbeard » Mon Jun 22, 2020 7:17 pm

So that could be why we have alot of problems with these air handlers that are wired this way. The manufacturer says we don't know what where talking about.

CoMod
Site Admin
Posts: 3975
Joined: Thu Feb 16, 2006 3:25 pm
Location: Russia
Contact:

Re: [?]: 24vac PLC inputs ?

Post by CoMod » Thu Jun 25, 2020 1:39 pm

1. SIMATIC ET 200SP, digital input module, DI 8x 24 V AC...48 V UC
https://support.industry.siemens.com/cs ... 6cf00-0au0
6ES7131-6CF00-0AU0
ET 200SP, DI 8x 24VAC..48VUC BA, PU 1
(sdoc) https://support.industry.siemens.com/cs ... /109759596

2. use buffer relay, 24vac LZX:PT570524
https://support.industry.siemens.com/cs ... 3Apt570524