dear all,
i have cpu 315-2dp and ET200S ( IM151-STANDARD ) " 6ES7 151-0AA04-0AB0 "
i tried to to establish communication by profibus dp between each other but i got the following message in hardware diagnostic for IM151( inserted and configured module types are not similar )
despit i selected the same part number from hardware catalog.
could any one can help me in this subject please urgently?
Regards,
Maher
[?]: ET200S communication problem
Re: [?]: ET200S communication problem
Show:
- HWConfig screencopy
- photo with PLC and ET200S Profibus connectors
- HWConfig screencopy
- photo with PLC and ET200S Profibus connectors
Re: [?]: ET200S communication problem
Thank you very much
Problem is solved when i add the termination bus module .
REGARDS,
Maher.
Problem is solved when i add the termination bus module .
REGARDS,
Maher.