Dear All
I have Siemens CPU 315-2DP and I want to use memory word variables I start from address MW 0,
I ask about the upper limit of MW variables addressing ?
i.e. can I use the address MW 300?
Thanks
[?]: Siemens CPU 315-2DP MW memory area
Re: Siemens CPU 315-2DP
Hi,
The CPU 315-2 DP has 2 kB memory for flags. So you can use flag words from MW0 to MW2046. Mind the retentivity.
Greets
Lepes9
The CPU 315-2 DP has 2 kB memory for flags. So you can use flag words from MW0 to MW2046. Mind the retentivity.
Greets
Lepes9
Re: Siemens CPU 315-2DP
Find your CPU and see Technical Data
Re: Siemens CPU 315-2DP
Here: https://eb.automation.siemens.com/mall/ ... atalogTree and select Product Information.
Greets
Lepes9
Greets
Lepes9
-
- Posts: 236
- Joined: Sat Oct 22, 2011 7:12 am
Re: [?]: Siemens CPU 315-2DP MW memory area
Thank you very much friends