Dear All
I need to read 2 wires analog input 4-20 mA signal in S7 SIMATIC Manager OB1
1- I bring analog input module and put the selector to D position.
2-Connect the module in rack and the address in HW config. start with 272.
3-connect a 20 pin front connector and connect screw 1 to 24 VDC (external power supply) and screw 20 to GND (from the same external power supply and from the rack power supply "307") this mean I make a major ground for the system.
4-I connect the input to the screws 2 "+" and 3 "-" (this input taken from analog output module in another PLC)
5-I wrote a network in OB1 just MOV instruction to move PIW 272 to MW100
but the result is 7FFF "Hex" when I try to read signal from module (by right click the module in HW config. and select Monitor/ Modify the result also is 7FFF "Hex" I replace the module the result still the same.
What can I do?????????????????????
Thanks a lot.
[?]: Siemens S7 300 analog input 4-20 mA signal
-
- Posts: 236
- Joined: Sat Oct 22, 2011 7:12 am
Re: [?]: Siemens S7 300 analog input 4-20 mA signal
make a variable table,put the mw there and then you can make it to dec
Re: [?]: Siemens S7 300 analog input 4-20 mA signal
Check the diagnostic list of the module, something is wrong (wire break, overflow etc.). (HW-congfig, highlight module, CTRL-D for diagnosis)
Greets
Lepes9
Greets
Lepes9
Re: [?]: Siemens S7 300 analog input 4-20 mA signal
You parameterized input in the HW config as a 2-wire current?
Modul order number?
Check the polarity of the connected device.
Modul order number?
Check the polarity of the connected device.
-
- Posts: 236
- Joined: Sat Oct 22, 2011 7:12 am
Re: [?]: Siemens S7 300 analog input 4-20 mA signal
Dear All
First of all "Thank you for helping"
the second thing what can I say???????? I Connect the jumper "in analog module" in B position instead of D position and I thoght I put it in D position
First of all "Thank you for helping"
the second thing what can I say???????? I Connect the jumper "in analog module" in B position instead of D position and I thoght I put it in D position