[?]: Connection to redundant PROFIBUS network 400H

Post by Schtiel » Sun Dec 20, 2009 5:15 pm

Is it possible to connect PROFIBUS slave to redundant PROFIBUS network without Y-Link module? Please help.
Можно ли подключить профибас-устройство к резервированной шине без модуля Y-Link? Есть ли какие-нибудь решения?

dsekulic
Posts: 186
Joined: Sun Feb 12, 2006 5:47 pm
Location: Europe

Re: [?]: Connection to redundant PROFIBUS network 400H

Post by dsekulic » Mon Dec 21, 2009 7:44 pm

Hi,
You have to know what nonredundant slave You want to connect to redundant network. For example ET200M have interface module which can connect to redundant network (IM153-2). Also there is possibilities to connect skave to just one CPU but this is not helpful because You don't know which CPU will be master at each time instant.
regards

globe
Posts: 3
Joined: Tue Dec 20, 2005 8:48 pm
Location: Europe

Re: [?]: Connection to redundant PROFIBUS network 400H

Post by globe » Tue Dec 22, 2009 10:03 pm

Perhaps this is what you looking after?