PLC SIM and simulation of PEW

Post by PLC_ITA » Wed Oct 28, 2009 5:12 pm

Hi collegues, how i can simulate a pew whit PLC SIM ?
I have a 412 cpu whit 3 analog in card. If i put an addres greather than Pew 256 ( or Ew256 ) a not valid will apper.

Anyone have a suggest for me ?

thank you

Homeroid_BL
Posts: 259
Joined: Fri Apr 03, 2009 3:24 pm
Location: Bosnia and Herzegovina

Re: PLC SIM and simulation of PEW

Post by Homeroid_BL » Wed Oct 28, 2009 5:33 pm

PIW addresses must exist in Your hardware configuration. See attachment. Work fine in my configuration.
Image

PLC_ITA
Posts: 263
Joined: Sat May 27, 2006 6:46 am
Location: Europe

Re: PLC SIM and simulation of PEW

Post by PLC_ITA » Wed Oct 28, 2009 6:39 pm

I know that the PIW are included into the hardware configuration.

I have reload a old projec whit a 315 cpu and all working fine, but if i use a 317 or a 400 series
if i write a piw gerathe than 254 , a "not valid" message apper on the top of the Input window

I dont know why

Is'nt a big problem, i copy my block into a projet whit 315 cpu and play... but ...

-----

Another problem : I have only a real cpu in my office, and now whit the customer i want to test the software.
I can force digital input whitout problem but i have te same problem, like PLCSIM : i can't write a value
into a piw or iw greather then 254 .
anyone have an idea ?
For further info i have a cpu 412

thank you

CoMod
Site Admin
Posts: 3975
Joined: Thu Feb 16, 2006 3:25 pm
Location: Russia
Contact:

Re: PLC SIM and simulation of PEW

Post by CoMod » Wed Oct 28, 2009 6:47 pm

PLC SIM/Step7 Version number ?

dsekulic
Posts: 186
Joined: Sun Feb 12, 2006 5:47 pm
Location: Europe

Re: PLC SIM and simulation of PEW

Post by dsekulic » Thu Oct 29, 2009 8:49 am

Hi,
I try to test with Your configuration (CPU412) and on my pc all work without any problems. For test i put
l piw512
t mw0
and change piw512 in plcsim with slider. I can see all changes in STEP7 when I turn on monitoring, I have STEP7 5.4 SP4 and PLCSIM 5.4 SP3
Did You download Your hardware configuration?
regards