Search found 81 matches

by NowanH
Sat Jul 25, 2015 1:52 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: HELP errror importing FTView ME in to SE Application
Replies: 1
Views: 3042

Re: HELP errror importing FTView ME in to SE Application

Probably that display is using some features not supported in FTView Studio 6.1.
by NowanH
Sun May 31, 2015 12:06 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: sharing tags between CompactlogixL35E
Replies: 6
Views: 8188

Re: sharing tags between CompactlogixL35E

Possible Causes for MSG Error Code 16#0004, IOI Syntax Error: - The message path. For example, when messaging to a CompactLogix processor. If you don't put a 1,0 at the end of the path. The error means you are getting to something partially valid, but not complete. Make sure the path is pointed to t...
by NowanH
Sat May 30, 2015 11:54 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: 1769-L32E firmware
Replies: 2
Views: 3152

Re: 1769-L32E firmware

Some questions: a) If the PLC connected to an ethernet network? (it´s better connect the PLC directly to the computer). b) Are you using any firewall/antivirus in your computer? Some ideas: - Try using the serial port of the PLC. - Try using a lower firmware version. - Try using other computer. In t...
by NowanH
Sat May 30, 2015 11:39 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: urgent HELP for PLC 1769-L32E and PANELVIEW PLUS 1000
Replies: 2
Views: 3341

Re: urgent HELP for PLC 1769-L32E and PANELVIEW PLUS 1000

please help with some questions! it is URGENT! I really don´t like when people say "it´s urgent". I'm only answering because the information could be helpful to other users. 1. Remove message from HMI screen (picture below) What does message mean? It is so serious message? What this message can say...
by NowanH
Fri Feb 06, 2015 3:15 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: rslogix 5000 v20.01 or higher
Replies: 7
Views: 33950

Re: rslogix 5000 v20.01 or higher

Hi , i need to download the version 20.01 or higher because the 19 doesn´t open my old files , someone has any idea of where i can download it with crack? or serial/keygen. Thanks. If you want to open an old application, you need to search for an old RsLogix. I mean, higher versions of RsLogix can'...
by NowanH
Fri Jan 30, 2015 3:08 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: RSLINX 1747-PIC driver problem
Replies: 5
Views: 7329

Re: RSLINX 1747-PIC driver problem

This is a procedure I found. Not sure if it works. 1. Obtain "serenum.sys" from XP sp2. It lives in C:\Windows\System32\Drivers and can be identified from it's file version (it will be file version 5.1.2600.2280). 2. Back up your existing "serenum.sys" under sp3 (it will be file version 5.1.2600.55....
by NowanH
Thu Jan 15, 2015 11:57 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: RSLogix 5000 - error: failed to go online with the controlle
Replies: 4
Views: 13556

Re: RSLogix 5000 - error: failed to go online with the contr

Anyone please help. I'm sure this problem is common. I don't think so. In fact, this is the first time I read about that kind of problem. You are trying to download an application to RSEmulate 5000 v20 using RSLogix 5000 v20 and the software says that the controller is no longer supported. Since I ...
by NowanH
Wed Jan 07, 2015 11:45 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: rsNetworx online issue
Replies: 1
Views: 2055

Re: rsNetworx online issue

It's not possible. According to Rockwells' knowledgebase: It is not supported to browse from DF1 to ControlNet. This is because the DF1 packet is much smaller than a ControlNet packet and could cause timeout errors, including the error seen above. If possible, use an ethernet module to make this con...
by NowanH
Mon Dec 29, 2014 11:51 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: Panelview plus6 1000 HMI tag
Replies: 2
Views: 2853

Re: Panelview plus6 1000 HMI tag

"#1" is a tag placeholder than can be replaced dinamically with any "real" tag. Suppose you have several areas in a process and you want to represent those areas in a panelview: a) In the traditional way, you create the first display and populate it with tags. Then you duplicate that display and cha...
by NowanH
Sat Dec 27, 2014 4:34 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: RSView32 6.40 Activation :-
Replies: 2
Views: 3462

Re: RSView32 6.40 Activation :-

That message appears when you try to open a project with an older version of RSView32 that the project was created with.
by NowanH
Sat Dec 27, 2014 4:27 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: micrologix 1500 problems sofware
Replies: 1
Views: 2312

Re: micrologix 1500 problems sofware

Firstly, you need to use RsLogix 500 to be able to download or upload applications from Micrologix 1500: http://www.mrplc.com/kb/How-to-Connect-to-an-Allen-Bradley-Micrologix-1500-using-RS-232-%28DF1%29_65.html RSLogix Emulate 500 only works on Windows XP SP2 and Windows 2000 Pro SP4: http://compati...
by NowanH
Tue Dec 16, 2014 8:18 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: PLC AB compactlogix L35E y HMI Proface GP2500
Replies: 3
Views: 3378

Re: PLC AB compactlogix L35E y HMI Proface GP2500

I was thinking about explaining you how to use Map PLC/SLC Messages command in RSLogix but I'm so lazy that I wrote "Application Note #1176: Mapping Native Tags for Access by GP-Pro" in Google. The first item in the list was a pdf document by ProFace explaining what you want to do.
by NowanH
Thu Nov 13, 2014 3:47 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: Factory talk ME verion 8.00
Replies: 6
Views: 8125

Re: Factory talk ME verion 8.00

a) You need a license for each monitor (at least if the final user wants to be in the legal zone). b) You can design displays as templates, and then use placeholders to populate them with data. But so far as I know you can not surpass the maximum number of tags declared in the license. c) In panel v...
by NowanH
Thu Nov 13, 2014 2:32 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: FactoryTalk View SE Two Monitors
Replies: 1
Views: 2360

Re: FactoryTalk View SE Two Monitors

Here 3 different ways:

1. You can run two different instances of the client (one instance running in each monitor).
2. Use x,y coordinates to make appear some displays in monitor #1 and other displays in the monitor #2.
3. Programming wide displays that uses both monitors from the beginning.
by NowanH
Fri Oct 10, 2014 12:18 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: Rslinx - problems to install in win 8
Replies: 1
Views: 2388

Re: Rslinx - problems to install in win 8

According with Rockwell webpage, RsLinx is compatible with all versions of Windows 8, except: - Windows 8.1 Industry Professional 64-bit - Windows 8 (home) 64-Bit - Windows 8 (home) 32-Bit First check that your version doesn't appear in this list. Installing RsLinx is a very straightforward procedur...
by NowanH
Fri Sep 05, 2014 11:17 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: Firmware upgrade problems
Replies: 5
Views: 8429

Re: Firmware upgrade problems

Make sure to point at the first instance of the controller in the USB or AB_VBP driver when selecting processor in RSWho window in ControlFlash. @Serge_n: in controllogix you can use rs-232, usb or even ethernet (if you have an ethernet module in the rack) for firmware upgrade. I always use ethernet...
by NowanH
Mon Aug 18, 2014 11:54 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: PLC's - CompactLogix L35E
Replies: 1
Views: 3055

Re: PLC's - CompactLogix L35E

"Non-registered class" means something was wrong in Windows Register related to RsLogix installation. You need to:

a) Uninstall RsLogix.
b) Restart the PC.
c) Run CCleaner or other similar app to clean windows register.
d) Restart the PC.
e) Install RsLogix.
by NowanH
Fri Jul 11, 2014 10:37 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: [Fishing ?]: RSLogix 5000 - Removing source protection
Replies: 52
Views: 97635

Re: [Fishing ?]: RSLogix 5000 - Removing source protection

The information you are looking for is in the previous posts. Please read from the first post.
by NowanH
Wed Jun 04, 2014 3:15 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: [LINK]: Allen Bradley AI2 software
Replies: 4
Views: 6147

Re: [LINK]: Allen Bradley AI2 software

Looking in Rockwell's knowledgebase I found note 9853: 9853 - 6200-PLC2 Installation Disk Images Access Level: Everyone Date Created: 10/29/2001 10:31 AM Last Updated: 02/18/2013 02:29 PM https://rockwellautomation.custhelp.com/app/answers/detail/a_id/9853 At the end of that note there are links to ...
by NowanH
Tue Jun 03, 2014 12:18 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: Studio 5000 go online not possible
Replies: 2
Views: 2700

Re: Studio 5000 go online not possible

Hi, so when i try to connect (EtherNetIP) i get everytime the same message http://www.directupload.net/file/d/3642/qfr56p4h_jpg.htm i have updatet the firmware for the logix 5555 (1756-L55 / 1756-M13) but the same message?! have anyone a idea?! greetings Your controller has firmware 16. Then you ne...
by NowanH
Tue Jun 03, 2014 12:05 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: Factorytalk View History
Replies: 4
Views: 11724

Re: Factorytalk View History

Dear NowanH I have not a user called sa in my computer (I install SQL from factorytalk view DVD) Do you have a simple way to make log file and print history without SQL Server? Thanks sa is not part of Window's users but SQL Server's users. If you installed SQL Server from FTView DVD then you have ...
by NowanH
Mon Jun 02, 2014 3:59 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: Factorytalk View History
Replies: 4
Views: 11724

Re: Factorytalk View History

a) First, you have to check what user you are using to log in: don't use Window's users. It's better to use the default user sa . b) By default SQL Server Express installs with an instance name of "SQLEXPRESS" or "MSSQLSERVER". If you are using a named SQL instance, you will need to specify the inst...
by NowanH
Mon Jun 02, 2014 1:17 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: Search some User Guides or Instructions about Allen Bradley
Replies: 2
Views: 2305

Re: Search some User Guides or Instructions about Allen Brad

Go to Allen Bradley/Rockwell website:

http://www.rockwellautomation.com/literature/

Manuals and other documents are free to download.
by NowanH
Thu May 22, 2014 8:03 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: Logix CPU Security
Replies: 5
Views: 4922

Re: Logix CPU Security

shkoko2000 wrote:send me the file and i will send u the passwords my mail is eng.hashemali@yahoo.com
If you read the OP, the CPU is locked and there is no backup application.
by NowanH
Tue May 20, 2014 2:47 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: Request for FactoryTalk ME 6.0 and Factory Task ME Station
Replies: 2
Views: 3007

Re: Request for FactoryTalk ME 6.0 and Factory Task ME Stat

If you have a legitimate license then go to Rockwell webpage:

http://compatibility.rockwellautomation ... ?crumb=112

Using your Registered Company Name and Software Serial Number is possible to download the software you need.
by NowanH
Sun May 11, 2014 9:49 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: .NET Access To Logix
Replies: 4
Views: 3829

Re: .NET Access To Logix

I'm not even sure OPC is the most efficient way to go here, are there any other better options for exchanging data more efficiently with all the AB, Siemens, Omron, etc PLCs? Is there a common communication language that all flavors would utilize? And most importantly, do they support .NET programm...
by NowanH
Fri May 09, 2014 12:48 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: .NET Access To Logix
Replies: 4
Views: 3829

Re: .NET Access To Logix

The answer depends of what you want to do. For quick testing, I use RsLinx Classic as an DDE server and Microsoft Excel or OPenOffice Calc as clients (this programs have embedded function to read DDE servers). For example, during any project's commissioning I use a spreadsheet with the I/O matrix li...
by NowanH
Wed Apr 30, 2014 7:29 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: MVI56E-MCM. Modbus. Analog signals
Replies: 2
Views: 3024

Re: MVI56E-MCM. Modbus. Analog signals

You are looking for the answer in the wrong place. The modbus module only get INT words because that is part of the standard. You have to go to the instrument's datasheet and see how it's built the communications table. For example: 3000: Pressure (High) 3001: Pressure (Low) This means that the inst...
by NowanH
Wed Apr 30, 2014 6:55 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: Problem with controller's time
Replies: 1
Views: 1633

Re: Problem with controller's time

Do you have other chassis where you can test the CPU running your application? I think you need to discard any problem in the chassis and other modules. Then you can return here to share your observations.
by NowanH
Wed Apr 30, 2014 6:47 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: Logix CPU Security
Replies: 5
Views: 4922

Re: Logix CPU Security

... that I want to mess with but I don't know the password Fixed that for you. Vendors lock PLCs for two reasons: 1. To protect their intellectual property. 2. To stop idiots messing with the code and killing themselves, or other people. 3. To hide the fact there is nothing special or magical in th...