Search found 3 matches
- Thu Jan 24, 2019 8:31 am
- Forum: Other PLC
- Topic: How to configuration for Momentum Communication 170 PNT 110
- Replies: 4
- Views: 2758
Re: How to configuration for Momentum Communication 170 PNT
The connection via Modbus+ is not so easy to realize as Interbus, you need to know what is peer-cop communication. You configure the base 1 in concept, the base 2 will be not configured in concept at all - I mean you don't see the 170PNT and 170ADM in Concept. Both bases are connected or communicat...
- Fri Nov 23, 2018 4:40 pm
- Forum: Other PLC
- Topic: How to configuration for Momentum Communication 170 PNT 110
- Replies: 4
- Views: 2758
Re: How to configuration for Momentum Communication 170 PNT
Hi Danhtran, well, the 171CCC76010 is the PLC and 171ADI35000 is the IO - put both together and the base 1 is ready. For base 2 take 171INT1100 and 170ADM35000 - put both together and connect to base 1 via IO-Bus (Interbus) cable. The communication adapter 170PNT for modbus+ can't be installed on b...
- Thu Nov 22, 2018 2:37 pm
- Forum: Other PLC
- Topic: How to configuration for Momentum Communication 170 PNT 110
- Replies: 4
- Views: 2758
How to configuration for Momentum Communication 170 PNT 110
Dear Experts, I'm a newbie for Momentum PLC. Please support me with the below situation: I'm trying to program a Modicon Momentum PLC, the entire system of the momentum as below: 1. Station 1: - Modicon Momentum Processor 171 CCC 760 10 - Communication Adapter Momentum 171 INT 110 00 - I/O base: Mom...