cavayiro wrote:...I wanna do some tests in RSlogix or any others program (simulation) to know if it will nice for my system or not.
You're looking for a pink unicorn.
by NowanH
Wed Apr 27, 2016 7:00 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: analog inputs outputs in rsemulate 5000 v20
Replies: 2
Views: 2841

Re: analog inputs outputs in rsemulate 5000 v20

RSEmulate 5000 doesn't support the modules used on ControlLogix/CompactLogix. You only have a virtual digital module, no analog module. If you need to test analog signals, try: a) SoftLogix (I think RA is not developing it any more). b) Write some logic to simulate internally the analog signals. c) ...
by NowanH
Mon Feb 08, 2016 8:18 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: Micrologix 1500: No response from processor at selected path
Replies: 4
Views: 6184

Re: Micrologix 1500: No response from processor at selected

Try again starting RSLogix 500 while holding the CTRL+Shift buttons.
by NowanH
Mon Feb 01, 2016 9:13 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: Panel View 600 project problem
Replies: 3
Views: 2953

Re: Panel View 600 project problem

No, you need FactoryTalk View Machine Edition for opening .apa projects.
by NowanH
Thu Jan 28, 2016 8:24 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: Panel View 600 project problem
Replies: 3
Views: 2953

Re: Panel View 600 project problem

Bad news: without the missing information you can't open the file for edition. So far I know there's no solution.
by NowanH
Wed Jan 20, 2016 3:31 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: [request] get .acd file from PLC without RSLogix
Replies: 1
Views: 2100

Re: [request] get .acd file from PLC without RSLogix

olloy wrote: If there is any way to get PLC project file from Allen Bradley with no RSLogix/Studio 5000 installed?
No, you need RSLogix.
by NowanH
Mon Jan 18, 2016 3:41 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: Re: Runtime in rsview ME v4.0!
Replies: 3
Views: 2967

Re: Runtime in rsview ME v4.0!

Rockwell Automation supports only the Full Installation of Windows Server 2008/Windows Server 2008 Release 2, Standard Edition . Please read TN 116943 FAQ: Rockwell Automation and Microsoft Product Compatibility (Access Level: Everyone) : https://rockwellautomation.custhelp.com/app/answers/detail/a_...
by NowanH
Fri Jan 15, 2016 12:04 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: Re: Runtime in rsview ME v4.0!
Replies: 3
Views: 2967

Re: Runtime in rsview ME v4.0!

help : the runtime in rsview Me v4.0 dont work ... please help It's very difficult to help you if you don't give more information: - What OS are you using? - Did you recently upgrade the OS? - Where's the problem? Running the runtime on the panel view? Testing the runtime on the PC? - Were you usin...
by NowanH
Thu Jan 14, 2016 12:45 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: FT 7 Studio - Cannot connect to addin object" 80004005
Replies: 4
Views: 4835

Re: FT 7 Studio - Cannot connect to addin object" 80004005

You're right. FTView 7 is not compatible with Windows 10. You always can verify compatibility in Rockwell's website, going to Support > Compatibility & Downloads.


http://compatibility.rockwellautomation ... 1487,51486
by NowanH
Wed Jan 13, 2016 1:11 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: FT 7 Studio - Cannot connect to addin object" 80004005
Replies: 4
Views: 4835

Re: FT 7 Studio - Cannot connect to addin object" 80004005

Since you are not giving more information like: Operative system. FTV is a new installation? FTV was working ok for several weeks/months? Do you installed the FTV patches? Other .NET applications in your PC are working correctly? I only can give you some general recommendations: If RSLinx Enterprise...
by NowanH
Tue Jan 05, 2016 12:25 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: Migrate RS Logix 500 to RS Logix 5000 with comment
Replies: 2
Views: 2668

Re: Migrate RS Logix 500 to RS Logix 5000 with comment

Read this Rockwell Technote (Access Everyone): 21962 RSLogix 5000 Translation Tool v1 and v2.0, a howto. https://rockwellautomation.custhelp.com/app/answers/detail/a_id/21962 You will find there a link to the Reference Manual (1756-RM085B-EN-P) "Converting PLC5 or SLC 500 Logic to Logix5550 Logic" a...
by NowanH
Fri Dec 25, 2015 9:06 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: Factroy talk SE v8.0 screen problem
Replies: 5
Views: 3777

Re: Factroy talk SE v8.0 screen problem

Some questions:

1. In the picture you uploaded, is the background display (the shrunken one) a separated display from the menu bar and the alarm banner?
2. What are the dimensions of the background display in pixels? What is the resolution of the client monitor?
by NowanH
Fri Dec 25, 2015 8:50 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: Not able to make object "VBA contolled" (sos)
Replies: 1
Views: 1743

Re: Not able to make object "VBA contolled" (sos)

1. I want to change the object (FT View SE v8.0) property to "VBA controlled". But its not allowing me to do it, like as you can see on the pic. Some objects don't support all the properties. Panel object doesn't support Vba controlled property. 2. I want to make an array of objects in FT View like...
by NowanH
Fri Dec 25, 2015 11:39 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: Factroy talk SE v8.0 screen problem
Replies: 5
Views: 3777

Re: Factroy talk SE v8.0 screen problem

It's difficult to repeat that behavior without knowing what method you are using for invoking the popup screens:

a) Are you using normal buttons, action is Run command and Press action is Display yourpopup?
b) Are you using VBA code?
by NowanH
Fri Dec 25, 2015 11:24 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: Popup windows on the FT View 8
Replies: 7
Views: 4884

Re: Popup windows on the FT View 8

In your case, it will work only once when that screen is open; on which you have put your Numerical Display. That screen should be updating all the time no??? so that is can detect all the times. This method works all the time and not only when the screen is open. It's because the Numeric Display i...
by NowanH
Fri Dec 25, 2015 2:55 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: Popup windows on the FT View 8
Replies: 7
Views: 4884

Re: Popup windows on the FT View 8

I think your code is similar to opc group. I will test it later. There is another way to show a popup when a tag changes its value. a) First you need to put an invisible numeric display in all the displays. In my projects, I always use a global object as a header with common information for all disp...
by NowanH
Fri Dec 25, 2015 12:47 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: Fail to upgrade firmware AB PLC 1769-L23E
Replies: 1
Views: 1729

Re: Fail to upgrade firmware AB PLC 1769-L23E

If cycling controller power it's not possible to complete the upgrade, then return the controller for factory repair.
by NowanH
Wed Dec 23, 2015 1:59 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: Store User Program to Compact Flash Memory Card
Replies: 4
Views: 3063

Re: Store User Program to Compact Flash Memory Card

I already switch the controller to Rem/Prog mode as mention in the Rockwell Manual. Is that MUST be in Program mode instead of Rem/Prog Mode? If you are using the key, you can return it to Rem/Prog position after switch to Program. You also can use Studio5000 (former RsLogix) to change the controll...
by NowanH
Tue Dec 22, 2015 7:53 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: Store User Program to Compact Flash Memory Card
Replies: 4
Views: 3063

Re: Store User Program to Compact Flash Memory Card

Please answer this: are you changing the controller to program while the controller properties window is open?

If the answer is yes, close the controller properties window, be sure that the controller is in program, and open the controller properties again. The button must be enabled now.
by NowanH
Fri Dec 18, 2015 12:19 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: Popup windows on the FT View 8
Replies: 7
Views: 4884

Re: Popup windows on the FT View 8

sachincool786 wrote:Done
Congratulations. Why don't you share your solution?
by NowanH
Sat Dec 12, 2015 7:27 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: Event logging in Factory Talk View SE v8.0
Replies: 1
Views: 2064

Re: Event logging in Factory Talk View SE v8.0

a) To be efficient, FTVSE needs to know what tags are going to be monitored and stored. So you have to provide that information one tag a time. Forget about a "log everything" command: it doesn't exist. b) I think that "to log each and every tag" is a poor approach. Logging everything is not only a ...
by NowanH
Tue Dec 08, 2015 10:31 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: Compactlogix via RSlogix 5000
Replies: 7
Views: 5073

Re: Compactlogix via RSlogix 5000

Can anyone show me example on how to use GSV instruction to read the processor type, serial number to display on HMI? 1. Open your RSLogix and go to Help > Instruction Help. Then look for Input/Output Instructions. Click on GSV button. There you have information about how GSV works. At the bottom o...
by NowanH
Mon Dec 07, 2015 6:28 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: Compactlogix via RSlogix 5000
Replies: 7
Views: 5073

Re: Compactlogix via RSlogix 5000

1) How to read the Processor data (Serial No and Type) of the Compact Logix CPU from RS Logix 5000? a) You can read that information using RSLinx. Locate the CPU and click on properties. b) You can access the controller properties by clicking on the Controller Properties in RsLogix. c) If you need ...
by NowanH
Mon Nov 16, 2015 10:22 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: 1394 Motor drive
Replies: 3
Views: 2915

Re: 1394 Motor drive

Go to Rockwell webpage -> Support -> Product Resources -> Literature Library and download GML Commander Troubleshooting Manual (GMLC-5.4-NOV99). From page 151: Q: I can’t get GML Commander to come online and communicate with the controller. What is wrong? A: There are many possible causes for this f...
by NowanH
Sun Nov 15, 2015 8:50 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: 1394 Motor drive
Replies: 3
Views: 2915

Re: 1394 Motor drive

Qamar wrote:I am new in PLC world pls tell me how we connect GML commander with 1394 drive
Go to Rockwell webpage -> Support -> Product Resources -> Literature Library and download GML Commander Reference Manual (GMLC-5.2-NOV99).
by NowanH
Thu Oct 22, 2015 12:03 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: RSVIEW32 32k runtime Open it to RSVIEW32 100K development
Replies: 2
Views: 3254

Re: RSVIEW32 32k runtime Open it to RSVIEW32 100K developmen

Both versions of RSView32 are installed in the same computer? What OS are you using? Are you trying to open an application previously backed up to CD or DVD? Most of the problems with database are related to CACHE folder and its privileges. That folder has to be writeable. You can delete all the fil...
by NowanH
Wed Oct 21, 2015 7:24 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: Can not upload from CompactLogix L33 ERM
Replies: 4
Views: 7293

Re: Can not upload from CompactLogix L33 ERM

Can not upload from CompactLogix 1769-L33ERM When I try - have error http://s8.postimg.org/t8e6j845d/N317_Belt_Conv_upl_ERROR.jpg What is wrong? Rev of PLC 21.011 Windows 7 Pro Studio 5000 Version 21.00 1. If you want to go online with a *Logix PLC, the firmware versions of the PLC and Studio 5K ha...
by NowanH
Fri Oct 09, 2015 3:05 pm
Forum: OMRON PLC & HMI
Topic: Omron PLC - Serial to ETHERNET/IP
Replies: 2
Views: 5066

Re: Omron PLC - Serial to ETHERNET/IP

Hi, I need get some data from a Omron PLC, model SYSMAC C200HX, this is an old plc that only have a serial port RS-232C. The fact is I need to convert and pass the serial data to ethernet/ip (from the plc to the pc). For this I found the advantech device ADAM-4571 that can get the data from serial ...
by NowanH
Tue Oct 06, 2015 6:03 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: REQUEST SOFTWARE AND COURSE ALLEN BRADLEY
Replies: 1
Views: 2832

Re: REQUEST SOFTWARE AND COURSE ALLEN BRADLEY

(dlink) Hello dears partner. I need the software RSLOGIX 500, RSLogix 5000 and it simulate software. if it is possible the factory talk. The version it doesnt matter, because only i need this software from learn to use it. I thank you for help me. Did you search in the forum before writing this pos...
by NowanH
Mon Oct 05, 2015 12:19 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: Interface plc with home devices
Replies: 4
Views: 3594

Re: Interface plc with home devices

Many thanks for your information, i want interface PLC with home devices like satellite reciever or UPS and read data from rsview32. (SCADA) for monitoring and control, but i dont know the AB module name for this type interfaces. Can please anybody help me for this issue. There are no specific modu...
by NowanH
Sun Oct 04, 2015 7:11 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: Interface plc with home devices
Replies: 4
Views: 3594

Re: Interface plc with home devices

You need to know what kind of port and protocol uses your device. For example: - Industrial UPS units have ethernet port and use Modbus TCP/IP. The manufacturers provide communication tables. - Old home UPS units had serial ports (I don't know what kind of protocols they used). Then you need to inst...
by NowanH
Thu Sep 24, 2015 12:13 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: SCADA Access to a Remote PLC
Replies: 3
Views: 4196

Re: SCADA Access to a Remote PLC

longquan wrote:Hi Everyone!
can Anyone help password to unprotected controlextendedlib 1.4.7 for compact control builder M version 5.1.1-2?
Thanks so much!
I would suggest you to open a new post in the correct forum.
by NowanH
Fri Sep 18, 2015 10:52 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: Controllogix 5000 bus expansion
Replies: 2
Views: 4029

Re: Controllogix 5000 bus expansion

You add a communication module to your main chassis and establish a network (controlnet, ethernet) to connect to other chassis or remote I/O. Since the secondary chassis and remote I/O are declared in the I/O tree of your project, you can manage their modules as if they were installed on the main ch...
by NowanH
Tue Sep 15, 2015 4:20 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: remove source protection in RSLOGIX5000
Replies: 3
Views: 6005

Re: remove source protection in RSLOGIX5000

Source protection only hides part of the logic. If you can't export to L5X, probably your application is protected with CPU Lock or RSMACC (FTV Assets).

In any case, you have to write for help in the post I provided to you. I think the OP (skdatmonster) could give you some advice.
by NowanH
Mon Sep 14, 2015 8:15 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: remove source protection in RSLOGIX5000
Replies: 3
Views: 6005

Re: remove source protection in RSLOGIX5000

hi dears. i have a source code (*.ACD) and want see this source , but this code is protected. i search in the internet and find the web site (https://github.com/skdatmonster/DecryptSourceProtection/blob/gh-pages/index.html) , but this not worked . any one can help to me for remove this protection (...
by NowanH
Sun Sep 13, 2015 11:46 am
Forum: OMRON PLC & HMI
Topic: OMRON CP1H same program not working with same new PLC
Replies: 2
Views: 8371

Re: OMRON CP1H same program not working with same new PLC

Probably the output on the new PLC is faulty (I mean, at hardware level). You can write a short program to test all of the outputs.
by NowanH
Sun Sep 06, 2015 8:19 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: [?]: How do I get data log from PVplus 1000?
Replies: 2
Views: 4234

Re: [?]: How do I get data log from PVplus 1000?

In PanelView Plus 6 you can use the FTP server and DataStore PLus Activex. I'm not sure if it's possible to install DataStore Plus in PanelView Plus.

http://theautomationblog.com/rockwells- ... ew-plus-6/
by NowanH
Sun Sep 06, 2015 8:10 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: emulate studio5000
Replies: 2
Views: 3005

Re: emulate studio5000

So far I know, the more recent version of RS Emulate is 24. In that case, Studio 5000 has no support for RS Emulate.
by NowanH
Sun Sep 06, 2015 8:03 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: MVI56-BAS Setting
Replies: 3
Views: 2691

Re: MVI56-BAS Setting

According to the User Manual, page 32: Download the new application to the controller and place the processor in run mode. If all the configuration parameters are set, the module’s Application LED (APP LED) should remain off and the backplane activity LED (BP ACT) should blink rapidly. Refer to Diag...
by NowanH
Mon Aug 31, 2015 8:47 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: MVI56-BAS Setting
Replies: 3
Views: 2691

Re: MVI56-BAS Setting

1. How many words did you write in Connection Parameters (input, output, configuration)? And Request Packet Interval (RPI)? 2. Where is located the module? In a remote chassis? 3. What is the status of the leds? 4. Can you connect to the module and download any basic application? 5. Was the migratio...
by NowanH
Sun Aug 23, 2015 2:15 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: Any Help Emulate 5000 Logix FT ect. Crack
Replies: 7
Views: 7999

Re: Any Help Emulate 5000 Logix FT ect. Crack

Skiroy wrote:Hello I am new here.
Welcome. Did you try using the search feature of this website?


viewtopic.php?f=12&t=18559&hilit=rs+emulate

viewtopic.php?f=41&t=15633
by NowanH
Fri Aug 14, 2015 6:49 pm
Forum: Other PLC
Topic: RSLogix 5000 - Functional block - can not open
Replies: 4
Views: 3870

Re: RSLogix 5000 - Functional block - can not open

The blocks are protected with source code protection feature. You can install this feature from RSLogix disk (it's inside Tools folder) but you need the password stablished by the original programmer to be able to unlock the blocks.
by NowanH
Fri Aug 14, 2015 6:42 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: I need help with PLC
Replies: 3
Views: 2635

Re: I need help with PLC

Some ideas: a) 1756-L62 has a serial port. You can configure the serial driver (DF1) in RsLinx and try to connect to the PLC. This method only works if the serial port in the PLC application is configured as slave (most of the programmers never touch the default slave configuration). b) If you are t...
by NowanH
Fri Aug 14, 2015 12:44 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: I need help with PLC
Replies: 3
Views: 2635

Re: I need help with PLC

You need to give more information. Something like:

a) CPU's model, firmware version.
b) Screenshot of the message you receive when you try to connect to the CPU using RSLogix.
by NowanH
Thu Aug 13, 2015 11:10 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: Complect of FactoryTalk
Replies: 1
Views: 3570

Re: Complect of FactoryTalk

There are two versions of FactoryTalk View Studio: 1. FactoryTalk View Studio for FactoryTalk View Enterprise (9701-VWSTENE): you can develop appplications for site edition and machine edition. 2. FactoryTalk View Studio for Machine Edition (9701-VWSTMENE): you can develop application ONLY for machi...
by NowanH
Tue Aug 04, 2015 11:02 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: How to install a Factory Talk View 5.1 into Windows 7.
Replies: 3
Views: 5873

Re: How to install a Factory Talk View 5.1 into Windows 7.

Please help me. Its possible to install the Factory Talk View Studio 5.1 into Win 7? Thanks. (read) According to Rockwell's Compatibility page, it`s not possible: http://compatibility.rockwellautomation.com/Pages/MultiProductCompareSelections.aspx?crumb=113&toggleState=&versions=50289,50287 In Rock...
by NowanH
Mon Jul 27, 2015 9:18 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: ControlNET problem
Replies: 5
Views: 3729

Re: ControlNET problem

I undestand that the problem is solved, right? In any case, about the cpu's firmware, please read the following document: http://literature.rockwellautomation.com/idc/groups/literature/documents/rn/1756-rn694_-en-p.pdf In page 3 and 4 you will find the Required Series and Firmware Revisions for Comp...
by NowanH
Mon Jul 27, 2015 11:58 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: ControlNET problem
Replies: 5
Views: 3729

Re: ControlNET problem

According to Rockwell's Product Compatibility & Download page, cpu L74 version 19 is not compatible with redundancy: http://compatibility.rockwellautomation.com/Pages/MultiProductCompareSelections.aspx?crumb=113&toggleState=&versions=52408,54160,52405,52406 You need to upgrade the CPU's firmware to ...