Search found 100 matches

by SE_support
Tue Apr 12, 2022 5:54 am
Forum: Other PLC
Topic: schneider Pro-Face LT3201
Replies: 1
Views: 668

Re: schneider Pro-Face LT3201

Hello, it looks you have to use GP-Pro Ex Software for LT3201:
https://www.pro-face.com/files/pdf/prod ... nual_e.pdf

If it doesn't start there is no way do save the application from HMI.
But may be it's only back light issue? What is the status of LEd on the front?

Best regards
by SE_support
Thu Apr 07, 2022 9:23 am
Forum: Other PLC
Topic: Schneider M238
Replies: 3
Views: 1149

Re: Schneider M238

You wish to download the application from the PLC, not to upload the application to the PLC.
Well, without upload information information on the PLC there is no way do download it.
Такая вот фигня.
by SE_support
Thu Feb 10, 2022 8:20 am
Forum: Other PLC
Topic: [?]: Unprotect Schneider PL7-Pro DFBs
Replies: 617
Views: 586435

Re: [?]: Unprotect Schneider PL7-Pro DFBs

Project pass is HNB@NISH
by SE_support
Mon Feb 07, 2022 1:24 pm
Forum: Utilites
Topic: tsx c usb 485 driver
Replies: 1
Views: 2157

Re: tsx c usb 485 driver

by SE_support
Thu Nov 18, 2021 10:10 am
Forum: Other PLC
Topic: Schneider TSX PLC Connection
Replies: 5
Views: 2619

Re: Schneider TSX PLC Connection

Hi, first of all you need to install and setup the unitelway driver. Then by using driver manager you need to setup the communication settings. Then you will be able by using driver manager to check the connection to the PLC. Only after that you can start the PL7 and try to estabsh the connection to...
by SE_support
Mon Aug 02, 2021 8:20 am
Forum: Other PLC
Topic: Please Help, looking for SE firmware 2.8 for M340
Replies: 2
Views: 947

Re: Please Help, looking for SE firmware 2.8 for M340

Hi, which one M340 PLC?
by SE_support
Fri Jan 15, 2021 7:11 am
Forum: Utilites
Topic: ELAN Memory card explorer
Replies: 0
Views: 2718

ELAN Memory card explorer

Hello all,

I'm looking for ELAN Memory card explorer software to be able to read data from PCMCIA card.
Thanks.
by SE_support
Thu Jan 14, 2021 7:23 am
Forum: Other PLC
Topic: Telemecanique TSX47 / who may read out program from cartridge?
Replies: 2
Views: 1276

Re: Telemecanique TSX47 / who may read out program from cartridge?

Hello Stefan, you got the answer already. Why to ask again the same question?
by SE_support
Wed Jan 06, 2021 9:03 am
Forum: Other PLC
Topic: [?]: Unprotect Schneider PL7-Pro DFBs
Replies: 617
Views: 586435

Re: [?]: Unprotect Schneider PL7-Pro DFBs

the files can't be downloaded.
by SE_support
Wed Jan 06, 2021 8:57 am
Forum: Other PLC
Topic: M580 SD CARD
Replies: 1
Views: 881

Re: M580 SD CARD

do you know which size exactly have BMXRMS004GPF card?
How do you wish to cone it, if PC doesn't recognize it as SD card?
by SE_support
Mon Dec 21, 2020 7:28 am
Forum: Other PLC
Topic: Schneider Systyem
Replies: 3
Views: 1495

Re: Schneider Systyem

What do really wand to know?
M580 and M340 Proxy communicate via Io Scanner or READ_VAR block - see youtube.

Just set Modbus+ and IP addresses for all hardware and also set the PLC address for M340 proxy - that is all.
It takes 5-10 minutes to get it working for someone, who knows this components.
by SE_support
Tue Dec 01, 2020 2:36 pm
Forum: Other PLC
Topic: [?]: Unprotect Schneider PL7-Pro DFBs
Replies: 617
Views: 586435

Re: [?]: Unprotect Schneider PL7-Pro DFBs

Sorry, there is no password. The password can be deleted, but you can't see the pass.
Please read the description on the first page how to remove the pass.
Sorry, I can't provide it.
by SE_support
Fri Nov 27, 2020 2:48 pm
Forum: Other PLC
Topic: [?]: Unprotect Schneider PL7-Pro DFBs
Replies: 617
Views: 586435

Re: [?]: Unprotect Schneider PL7-Pro DFBs

Pl7 Pro v4.5 SP5 - what else :)
Image
by SE_support
Mon Nov 23, 2020 9:45 am
Forum: Other PLC
Topic: Ecostruxure Control expert (Unity Pro V14)
Replies: 21
Views: 47347

Re: Ecostruxure Control expert (Unity Pro V14)

why not just download the software direct from www.se.com webpage?
by SE_support
Mon Sep 28, 2020 7:41 am
Forum: Other PLC
Topic: UnityPRO CANOpen
Replies: 1
Views: 824

Re: UnityPRO CANOpen

You will find huge amount of manuals directly on youtube extra for all, who hasn't time to read manuals.

https://www.youtube.com/watch?v=ZACdErCMnEM
by SE_support
Tue Jun 16, 2020 10:47 am
Forum: Other PLC
Topic: Trick using two plc simulator with Unity Pro13 - Same PC
Replies: 1
Views: 1009

Re: Trick using two plc simulator with Unity Pro13 - Same PC

The simulator doesn't simulate the communication, so no I/O scanner or read/write with SIM.
by SE_support
Tue Jun 16, 2020 7:37 am
Forum: Other PLC
Topic: Schneider Premium Non-modbus data exchange/
Replies: 2
Views: 1200

Re: Schneider Premium Non-modbus data exchange/

Можно, используя OpenTCP. Для этого понадобится TSXWMY100 модуль и библиотеки.
by SE_support
Wed Mar 11, 2020 3:51 pm
Forum: Other PLC
Topic: Ecostruxure Control expert (Unity Pro V14)
Replies: 21
Views: 47347

Re: Ecostruxure Control expert (Unity Pro V14)

Bad news for you, doesn't matter what you choose - the license is not more valid after that.
by SE_support
Thu Nov 28, 2019 3:07 pm
Forum: Other PLC
Topic: Ecostruxure Control expert (Unity Pro V14)
Replies: 21
Views: 47347

Re: Ecostruxure Control expert (Unity Pro V14)

please provide your original app, I'll have it converted.
by SE_support
Wed Jun 26, 2019 5:38 am
Forum: Other PLC
Topic: IO error on BMXAMI0810
Replies: 1
Views: 846

Re: IO error on BMXAMI0810

How have you configured the channels? In case of 4-20ma probably you have not wired all channels and get the broken wire error.
Anyway you can see the reason for error directly in UnityPro in online mode.
by SE_support
Mon Jun 17, 2019 7:01 am
Forum: Other PLC
Topic: Ecostruxure Control expert (Unity Pro V14)
Replies: 21
Views: 47347

Re: Ecostruxure Control expert (Unity Pro V14)

well well, just wait a little bit and your trial time is gone :)
by SE_support
Thu Mar 21, 2019 7:07 am
Forum: Other PLC
Topic: Unlock unity pro s v11.0 project
Replies: 1
Views: 1327

Re: Unlock unity pro s v11.0 project

Post your application and you will see.
by SE_support
Thu Dec 06, 2018 7:35 am
Forum: Other PLC
Topic: CPU 113 03 and Nom211 00(Modbus plus)
Replies: 4
Views: 2436

Re: CPU 113 03 and Nom211 00(Modbus plus)

Почитал документацию по Modbus+ и не нащел возможности обмена информации между двумя сетями без Bridge Plus.

Если есть проект HMI, то там в device manager можно посмотреть адрес частотника, тогда думаю будет понятно каким образом обменивалась инфо.
by SE_support
Wed Dec 05, 2018 8:55 am
Forum: Other PLC
Topic: [?]: Unprotect Schneider PL7-Pro DFBs
Replies: 617
Views: 586435

Re: [?]: Unprotect Schneider PL7-Pro DFBs

theo26220 wrote:Hi vlad2006gr

Can you help me with this? https://drive.google.com/open?id=1Mi4cp ... SwCIGeUjf5

thanks you much
Hi theo26200,

see PM
by SE_support
Wed Dec 05, 2018 8:46 am
Forum: Other PLC
Topic: CPU 113 03 and Nom211 00(Modbus plus)
Replies: 4
Views: 2436

Re: CPU 113 03 and Nom211 00(Modbus plus)

Привет RAGNAROG, у вас две независимые сети MB+ и нет возможности передавать данные из одной сети в другую на прямую. Можно настроить peer-cop в обоих сетях для быстрого обмена информации и использовать регистры PLC как буффер. Т.е. PLC производит обмен данными с частотником - buffer_1, NOM производ...
by SE_support
Mon Nov 26, 2018 6:50 am
Forum: Other PLC
Topic: How to configuration for Momentum Communication 170 PNT 110
Replies: 4
Views: 2759

Re: How to configuration for Momentum Communication 170 PNT

The connection via Modbus+ is not so easy to realize as Interbus, you need to know what is peer-cop communication. You configure the base 1 in concept, the base 2 will be not configured in concept at all - I mean you don't see the 170PNT and 170ADM in Concept. Both bases are connected or communicate...
by SE_support
Fri Nov 23, 2018 6:31 am
Forum: Other PLC
Topic: How to configuration for Momentum Communication 170 PNT 110
Replies: 4
Views: 2759

Re: How to configuration for Momentum Communication 170 PNT

Hi Danhtran, well, the 171CCC76010 is the PLC and 171ADI35000 is the IO - put both together and the base 1 is ready. For base 2 take 171INT1100 and 170ADM35000 - put both together and connect to base 1 via IO-Bus (Interbus) cable. The communication adapter 170PNT for modbus+ can't be installed on ba...
by SE_support
Thu Oct 04, 2018 10:41 am
Forum: Other PLC
Topic: Difference between RS232, RS485 , RS422
Replies: 1
Views: 1930

Re: Difference between RS232, RS485 , RS422

i am new in plc programming . i know the basics difference between the rs232, rs422, rs485. but i am little bit confused in it. so i have the following question regarding these terms. 1. can these protocols communicate with each other i mean rs232 can communicate with rs422 or rs485 and same. 2. my...
by SE_support
Fri Jun 29, 2018 6:00 am
Forum: Other PLC
Topic: quantum cpu113 и hmi панелька
Replies: 2
Views: 1396

Re: quantum cpu113 и hmi панелька

Привет ROGNAROG, адреса в Modbus можно записывать разным образом, точнее сказать формат записи зависит от разрботчика. Так например адрес 4000541 можно так же записать как 4:541 или 400541, а так же %MW541 - всё одно и тоже, т.е. адрес 451 holding register. HMI сам считает все нужные ему регистры с ...
by SE_support
Tue Apr 17, 2018 1:53 pm
Forum: Other PLC
Topic: Unity Pro XL **.stu ***.CTX
Replies: 1
Views: 2382

Re: Unity Pro XL **.stu ***.CTX

Hello. How do I know which version that I can use? I guess that shoud be a old version because verry old machine. The diffrent extension I have on the old backup I have recieved is Program.xml Program.xdm Program.XEF Program.STU Program.CTX Program.BAK When I try to open it with Unity Pro XL V12 I ...
by SE_support
Mon Apr 16, 2018 2:52 pm
Forum: Other PLC
Topic: Urgent communication between Schneider m340 and honeywell
Replies: 1
Views: 1491

Re: Urgent communication between Schneider m340 and honeywel

Hi accmpy,

on M340 side you can only setup the IP-address and %MWi variable addresses.
So, if communication doesn't work, then check the IP and %MWi addresses.
by SE_support
Wed Apr 11, 2018 3:26 pm
Forum: Other PLC
Topic: [?]: Unprotect Schneider PL7-Pro DFBs
Replies: 617
Views: 586435

Re: [?]: Unprotect Schneider PL7-Pro DFBs

sunshine wrote:hello Vlad,
please can you found the password of this projects, many thanks

https://mon-partage.fr/f/vCInUa1V/
https://mon-partage.fr/f/WRtbgLWX/
https://mon-partage.fr/f/TVRAq5Ed/
Hello sunshine, please check following info.
app pass: aeg2-kiabi
dfb pass: aeg2-kia

Best regards
by SE_support
Wed Apr 11, 2018 3:00 pm
Forum: Other PLC
Topic: [?]: Unprotect Schneider PL7-Pro DFBs
Replies: 617
Views: 586435

Re: [?]: Unprotect Schneider PL7-Pro DFBs

nene wrote:Hello Vlad i hope you doing great!!
please i need your help to find a password for DFBs




https://drive.google.com/file/d/1546-Ka ... sp=sharing
Hi nene, the DFB pass and app pass are the same: !M@rch?
Good luck!
by SE_support
Thu Mar 08, 2018 8:30 am
Forum: Other PLC
Topic: [?]: Unprotect Schneider PL7-Pro DFBs
Replies: 617
Views: 586435

Re: [?]: Unprotect Schneider PL7-Pro DFBs

Привет Vlad,

с помощью какого пароля я смогу сменить пароль на секции в данном проекте?

https://www.file-upload.net/download-13 ... pt.7z.html

Спасибо.
by SE_support
Thu Dec 14, 2017 2:45 pm
Forum: Other PLC
Topic: i need software to modicon please
Replies: 1
Views: 1462

Re: i need software to modicon please

I'm not sure, but I think you need the software for this plc like AKF programming software for DOS.
Some info you will find here: http://control.com/thread/1026172136
by SE_support
Thu Dec 14, 2017 2:29 pm
Forum: Other PLC
Topic: Эмулятор modbus rtu rs485
Replies: 1
Views: 1547

Re: Эмулятор modbus rtu rs485

Привет Ragnarog,

всегда думал, что симуляторы работают с COM портом, а уж какой адаптер и какая физика RS232/RS485 не играет роли.
Попробуй Generic Modbus/Jbus Tester.
by SE_support
Wed Dec 13, 2017 10:28 am
Forum: Other PLC
Topic: [?]: Unprotect Schneider PL7-Pro DFBs
Replies: 617
Views: 586435

Re: [?]: Unprotect Schneider PL7-Pro DFBs

Elecmoon wrote:Dear Experts, i have a Schneider plc program with a lock icon near the names of DFB's, i am Siemens plc programmer and this type of protection called (KNOW_HOW_PROTECT), i am new in Schnieder, can you help me?
Hello Elecmoon,

please provide your application
by SE_support
Fri Oct 06, 2017 12:23 pm
Forum: Other PLC
Topic: [?]: Unprotect Schneider PL7-Pro DFBs
Replies: 617
Views: 586435

Re: [?]: Unprotect Schneider PL7-Pro DFBs

Привет Vlad,

*****************
by SE_support
Wed Jan 18, 2017 9:48 am
Forum: Other PLC
Topic: How to connect to Quantum Schneider PLC can not see config
Replies: 4
Views: 2938

Re: How to connect to Quantum Schneider PLC can not see conf

Novice wrote: I think that in the PLC program the guy uncheck the check box Upload information on the project option
is it possible to find out this issues?
Yes, the upload information is missing.
by SE_support
Tue Jan 17, 2017 2:20 pm
Forum: Other PLC
Topic: How to connect to Quantum Schneider PLC can not see config
Replies: 4
Views: 2938

Re: How to connect to Quantum Schneider PLC can not see conf

I assume you are using UnityPro and Quantum is a highend Quantum PLC right? In this case if you try to upload the application from the PLC you will the application or will will get the message why it doesn't work. 1) which plc do you have? 2) which software do you use? 3) which error message did you...
by SE_support
Tue Nov 15, 2016 8:43 am
Forum: Other PLC
Topic: HeLP modicon m340 and ATV 212
Replies: 5
Views: 3377

Re: HeLP modicon m340 and ATV 212

Если уже работало, а теперь нет, то некоторые вещи можно исключить. Проверь следующее: 1) Когда идет опрос по Modbus/TRU, то на процессоре должен загораться LED "Ser" и в в твоём Array St_read_1 во втором слове (INT) будет записана ошибка 2) надеюсь ты не забыл указать timeout в Array St_read_1 в тр...
by SE_support
Mon Nov 14, 2016 12:43 pm
Forum: Other PLC
Topic: HeLP modicon m340 and ATV 212
Replies: 5
Views: 3377

Re: HeLP modicon m340 and ATV 212

Здравствуйте господа.Нуждаюсь в вашем совете.Как на ПЛК modicon m340 проверить работу порта Modbus serial port.кратко изложу суть проблемы пропала связь плк с ATV212.Смотрел в меню диагностику, обмена нет.Пробовали сбрасывать до заводских настроек не помогло,пробовали перезагружать приложение и пер...
by SE_support
Thu Sep 29, 2016 11:38 am
Forum: Other PLC
Topic: C++ and PLC
Replies: 6
Views: 4642

Re: C++ and PLC

Готовые библиотеки для C++ я к сожалению не видел и Schneider таковых не предлагает.
Знаю, что можно через NOE (через SOAP протокол) вести опрос и запись всех регистров напрямую через VBA или Excel.

Вот на этом сайте есть куча материалов по теме:
http://www.modbus.org/tech.php
by SE_support
Thu Sep 29, 2016 6:53 am
Forum: Other PLC
Topic: C++ and PLC
Replies: 6
Views: 4642

Re: C++ and PLC

Интересно было бы узнать по какому протоколу. Судя по всему %MW100 это всё-таки Schneider и протокол Modbus/TCP или?
by SE_support
Thu Aug 25, 2016 12:45 pm
Forum: Other PLC
Topic: [Support] Profibus Communication Basic Questions
Replies: 3
Views: 2894

Re: [Support] Profibus Communication Basic Questions

Hello Ali,

try to find anything by using google. I know this module very good, so I'm able to let it work with closed eyes :)
by SE_support
Tue Aug 23, 2016 11:50 am
Forum: Other PLC
Topic: [Support] Profibus Communication Basic Questions
Replies: 3
Views: 2894

Re: [Support] Profibus Communication Basic Questions

Hello Ali, I will try to answer some of your questions. 1) I have DB9 Female connector in both devices, what are standard pin-out for Profibus Communication. You don't need to know pinout, just open the DB9 profibus-connector and you will find only 2 color marked pins suitable for profibus cable. 2)...
by SE_support
Wed Aug 17, 2016 6:58 am
Forum: Other PLC
Topic: DEAD ERROR No. 305
Replies: 3
Views: 2288

Re: DEAD ERROR No. 305

ernandef wrote:Hello SE_support !

I solved this issue on other way. I opened my cpu and cleaned all connections inside. After that, the problem was solved.

Thank you!!
really strange solution :) May be you had luck. Thanks for feedback!
by SE_support
Mon Aug 15, 2016 8:41 am
Forum: Other PLC
Topic: DEAD ERROR No. 305
Replies: 3
Views: 2288

Re: DEAD ERROR No. 305

Hello ernandef,

in most cases you need to check/replace your power supply (140CPSxxxxx).
by SE_support
Tue Jul 19, 2016 5:58 am
Forum: Other PLC
Topic: [?]: Unprotect Schneider PL7-Pro DFBs
Replies: 617
Views: 586435

Re: [?]: Unprotect Schneider PL7-Pro DFBs

А зачем вам нужен пароль? 7:HKLD2013 = это зашифрованный пароль. Там стоит галка криптовать его. В этом проекте вы можете с помощью пароля A5Y5AQ199FQDE9K сменить пароль, и потом уже с новым паролем снять защиту. Основной пароль состоит из 10 знаков. Тот, который вы вводите, криптуется и потом уже ...